Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


IN MY INDUSTRIES 125 HP MOTOR USED FOR THAT ONLOAD AMPS UP
TO 280
SO CAN I USE ONE LOWER KVA DG SET WITH STEP UP TRANSFORMERS
THAT MEANS WITH LOW POWER INPUT TO GET CONSTANT HIGH POWER
OUTPUT
EG:125KVA DG SET = 250 KVA STEP UP TRANSFORMERS



IN MY INDUSTRIES 125 HP MOTOR USED FOR THAT ONLOAD AMPS UP TO 280 SO CAN I USE ONE LOWER KVA DG S..

Answer / sudhakar g

Generally if u take125HP if we converted in to KW it will come 93.75KW only we can use...

I=(93.75*1000)/(1.732*415v*0.8)

I=163A

this is the maximum current we can use at full Load then how you are using upto 280A....

I think it is not possible...Correct me if i am wrong...

In your second case it is not possible To genrate 125KVA DG set to 250KVA Stepup transformers bcoz if we saw in Generation or transmission of supply the 400KV or 200KV lines there we can use 3 MVA transformers for stepup or Stepdown bcoz the input sully is capable to genrate the supply higher or lower......
According to IS standards the distance between pits must be
2.5mtrs and from the building it should be far from 3000mm

I am taking Electrical desining classes in Bangalore...It
will be usefull for designing as well as site engineers
those who are intrested to go for Electrical
Engineers....we give you indepth knowledge of Load calu,
Cable sizing, Lighting cal, panels, breaker
selection,Autocad drawing....if any body intrested means
pls call to +91-7760362623 or sudhakar28485@gmail.com

Is This Answer Correct ?    2 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Define delay time.

0 Answers  


What are the causes of eddy current losses?

1 Answers   Schneider,


What is the criteria that generally follow by distribution licenses to fix contact demand of their industrial customers?

0 Answers  


How can we select suitable capacity generator for three phase load (inductive load) and how to take study analysis in 3 three phase load system ?

0 Answers  


how to set earth fault relay

1 Answers  


what is the current rating of 2500 KVA,33KV/433v transformer on secondary(LT) side

9 Answers   Reddy Labs, Vitrum Glass,


I Need standard operation procedure(SOP)for 500kva Oil type transformer oil filtration & Procedure for IR value checking.

0 Answers   Reliance,


what is phase to phase to phase to ground fault

1 Answers  


In Air circuit breaker LSIG protection unit is used. Without fault in cables (2 runs 3Cx150Sq.mm Copper, 1Kv grade, XPLE armored cable IR value is more than 550Mohm @ 500V Megger) and load section Long time Overcurrent protection is triggers and trips the unit. We changed LSIG protection with new factory tested unit. Even then fault is persisting. Please suggest the possible causes

0 Answers  


Direction of flow of active power and reactive power with logic?

0 Answers  


How to choose the vector group for the step up and step down transformers??? Tell me the which vector group is suitable for step up and step down transformers and whats the reason to choose and whats the benefits???

0 Answers   L&T,


hi plz send me reliance placement papers..i.e electrical technical papers that have been asked in reliance test.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)