IN MY INDUSTRIES 125 HP MOTOR USED FOR THAT ONLOAD AMPS UP
TO 280
SO CAN I USE ONE LOWER KVA DG SET WITH STEP UP TRANSFORMERS
THAT MEANS WITH LOW POWER INPUT TO GET CONSTANT HIGH POWER
OUTPUT
EG:125KVA DG SET = 250 KVA STEP UP TRANSFORMERS
Answer / sudhakar g
Generally if u take125HP if we converted in to KW it will come 93.75KW only we can use...
I=(93.75*1000)/(1.732*415v*0.8)
I=163A
this is the maximum current we can use at full Load then how you are using upto 280A....
I think it is not possible...Correct me if i am wrong...
In your second case it is not possible To genrate 125KVA DG set to 250KVA Stepup transformers bcoz if we saw in Generation or transmission of supply the 400KV or 200KV lines there we can use 3 MVA transformers for stepup or Stepdown bcoz the input sully is capable to genrate the supply higher or lower......
According to IS standards the distance between pits must be
2.5mtrs and from the building it should be far from 3000mm
I am taking Electrical desining classes in Bangalore...It
will be usefull for designing as well as site engineers
those who are intrested to go for Electrical
Engineers....we give you indepth knowledge of Load calu,
Cable sizing, Lighting cal, panels, breaker
selection,Autocad drawing....if any body intrested means
pls call to +91-7760362623 or sudhakar28485@gmail.com
Is This Answer Correct ? | 2 Yes | 0 No |
Can Dy11 and Dy1 vector group transformers be paralleled?
is dc transformer is possible ?
What are the uses of stepper motor?
what is sevice settings for mccb?How can be it setted?
why rating of motor in HP?
what is mean by PIR in circuitbreaker and give me detail of that?
What is resistance reading of earth copper rod with grid and without grid?
how much mininmum length required to conduct a DC Hipot Test on 33kV AC Cable with 45kV DC? Is it 20meter or Less then 20?
What are the two basic types of transformers?
if i have to use 14 kw what size of power cable can i use and size of earth cable also.
How you will determine the volume of oil in a particular Distribution transformer.
In our homes we place the 5Amps fuse...now in our house only takes 5Amps for all normal conditions ha???