Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Any one can explain if there is any harm from humming noise
heard from air circuit breaker : we have 415 switch board
having two incomers from transformers 3.3KV/415V , when bus
coupler closed, and open one ACB incomer to work in one of
the transformers, the current started hunting around 50
Amps, and heard humming noise from the air circuit breaker,
although the load current was only 1200 amps while the ACB
capacity is 2500 Amps, and the transformer 1600 KVA. The
same didn't happen when taken the other transformer offline.
Why this humming noise and current fluctuation? is there
any implication or danger, bearing in mind that we just
returned everything back to normal and stopped the
maintenance of the transformer. Shall we go ahead and
ignore this noise?

Answers were Sorted based on User's Feedback



Any one can explain if there is any harm from humming noise heard from air circuit breaker : we ha..

Answer / vijendra joglekar

First of all do you know what is the reoson for using
Circuit breaker in electrical equipment/device means it
will protect the device whenever the fault occurs it will
trip the breaker or open the contacts ( fixed /moving
contacts).And you told that there is some humming sound is
there in CB that means it will harm the equipment (may
chance to fire) just you need to check whether all the
contacts/connections in the breaker/device is tightly
connected by loose connections also you getting these type
of errors/faults even tho the current rating is samall (
you told 50A)
You need to check:
1.Tightness (mandotary)
2.Check the calibration of the equipment
2.Check the technical specification (i know you already
checked before installing)
Go ahead dont stop the work if you are still getting sound
means u just repalce the breaker unless why u r taking risk.

Is This Answer Correct ?    5 Yes 1 No

Any one can explain if there is any harm from humming noise heard from air circuit breaker : we ha..

Answer / hussain

Thanks Vijendra Joglekar
The breaker has been serviced already and nothing wrong
found, the load is 1200 Amps, but the current fluctuation
is around 50 Amps (+&- 25Amps)when load increased, the
sound started at load above 800 Amps, while the breaker is
rated up to 2500 Amps.

Is This Answer Correct ?    1 Yes 0 No

Any one can explain if there is any harm from humming noise heard from air circuit breaker : we ha..

Answer / k.prakashchandra

Check the hold coil, if it has any.

Is This Answer Correct ?    0 Yes 0 No

Any one can explain if there is any harm from humming noise heard from air circuit breaker : we ha..

Answer / yusuf

Can you tell me what is the circuit Breaker settings like
overload,shortcircuit,ground fault & Instantaneous s/c
settings.Acc to your details max load that can be derived
from X'mer is 2228.56 amps & from 800 amps onwards Breaker
is creating this problem.So around from 25% load CB is
creaing problem also tell me about any release installed
(Closing,shunt,undervoltage).

Is This Answer Correct ?    0 Yes 0 No

Any one can explain if there is any harm from humming noise heard from air circuit breaker : we ha..

Answer / hussain

This is an old breaker and has no protection devices, close
and open manually. closes by operating rod and opens by
trip button. Protection in the HV side of the transformer
incomer. I suspect the contacts got wear and tear due to
long time service and intending to change the fix and
moving contacts. Small gaps ( not seen by eyes) between
contacts could cause this sown as far as I know.

Is This Answer Correct ?    0 Yes 0 No

Any one can explain if there is any harm from humming noise heard from air circuit breaker : we ha..

Answer / yusuf

Yes,it can be.A very small gap can't seen by naked eyes
between CB main contacts could create this problem.Exactly
from which area this sound is comming? Is is some Clicking
sound/Buzzing sound.Can u give me Breaker details like make
(Siemens/L&T/ABB/Scneider) & Type no, 3pole/4 pole any
neutral earth fault protection provide extra to the
breaker,two breaker earthing & neutral connection.I am
talking of two main transformer breaker.Please furnish some
details to rectify the problem.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

we have a 2000kva step down transformer at our site. The HT side is charged from 22000V. So the primary current will be 52.48A. So why the HT breaker(SF6 ABB) is rated of 1250Amps ?

2 Answers  


what is the funda of earthing? Explain breifly about earthing?

5 Answers   IOCL,


in ct secondary one terminal is connected to earth why?

1 Answers  


can we use the step down transformer to step up transformer

6 Answers  


why magnetising curve not start with zero voltage?

0 Answers   TATA,


how can we understand that where we have to use ac or dc coil for solenoid valve and why?what is the different between coil of ac and dc explain please.

0 Answers   TK Group,


when the motor was star position that is running ok but when the motor was delta it was tripped? why?

5 Answers   Nimbus, SEL Manufacturing,


what is the diffrence between R Y B phase and why it is called RYB

5 Answers  


can u give me a brief idea about power line carrier communication ??

0 Answers  


Is it necessary to place tap changer in secondary winding or we can use on both sides?

3 Answers  


11 kv metering is done in my factory.Meter show PF 1.000 but kvarh lag&lead show 24&94 respectively & Avg.PF is .956 .? is what i do for inproove my PF to 1.000

3 Answers  


What is the use of arc chute in ACB?

7 Answers   lenovo,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)