How to protect the water pump by no load running.
Answers were Sorted based on User's Feedback
Answer / prakash
If your concerns with domestic water pump dry run control,
then you can use a floating switch at level point that can
be connected to series with DOL starter if already installed.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / jimmy
Just put level switch NC contact in series with overload
contacts in the Starter Circuit.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / kamal
By using under current relay , setting is no load current,
below this level it trip.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / parth belani
We can protect a pump from no load running by using a
minimum recirculation line. This line connects outlet with
the main tank or the inlet. so there will always be some
minimum flow through the pump.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sandip paithankar
put a moisture sensor in land which need to wet on starting and ending point of it.then give to transistor then micro controller do if else program and understand the condition of land it may wet or dry.then give command to relay to operate the water pump
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ks
by using the level transmitter and with out plc with some
no nc additional elements in the contactor it is possible
to control.
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / subrat.das1985
i think we can over come from this problem by using proximity sensor.or by using timer .
| Is This Answer Correct ? | 0 Yes | 3 No |
What is the use of starter in tube light fitting.how it works.
how to claculate the ups load in KVA pls give the if any fourmoul?
If you have an earth with pilecap then your resistance is really low. why and how?
Why electrical heaters are not provided with overload relays in circuits
Hi Recently I got one formula that is Impedence of Xformer = Rated KVA/Root 3 * secondry voltage OF Xformer. Is it Right??????
which type of motor complete it's one rotation in 30 day's.
What is CVT and what is relation with wave trap?
what is the calculation of current when a clampmeter is attached to two phases of any drives.
WTA used cb?
We are using 4 MVA transformer and we provided 2 separate earthing pit for Body and 2 separate earthing pit for neutral, can we connect separate body earthing pit to other earthing pit (Equipment earthing)?
if a train is running on a speed of 40 K MPH and crosses a individual passing by him in 48 secs who is riding a horse with a speed of 25 K MPH. what is the length of the train?
What is the Resposiblity of Electrical Utility Engineer
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)