FOR ELECTRICAL TRANSMISSION TOWER WHAT SHOULD BE THE MINIMUM
HEIGHT FROM THE GROUND? AND WHAT SHOULD BE THE DISTANCE
BETWEEN THE TWO CONDUCTOR?
Answer / k.prakashchandra
For extra high tension tr lines, the minimum clearance is
not less than 5.2 mtr+ 0.3 mtr for every 33 Kv or part
thereof by which the voltage of the line exceedes 33
Kv,provided that the minimum clearance along or across the
road shall not be less than 6.1 mtr.Clearances between
conductors for 66 Kv 75 cm,110 Kv- 125 cm ,132-160cm,220-
210 cm and 400Kv-410 cm
Is This Answer Correct ? | 5 Yes | 2 No |
we have a rewind motor of 2Hp,2800Rpm, 220Volt AC. how can we choose the running capacitor for this motor, any formula for that?
how to select the isolation tranformer for siemens 802dsl cnotroller
in conclusion why we select you?
while conducting an experiment why we connect the armature rheostat in maximum position and field rheostat in minimum position
why need of ac exietation in alternater.
From what on-site components does the HT panel monitoring the bus-bars in a 11kV system take inputs?
i am getting to neutral earth voltage zero ,is this a perfect earthing ?
i am confused about generator. i have generator of 380 KVA that is 304 KW by that formula KW=KVA*0.8... then by this formula I=KW/V*1.732*0.8 the amperes are 528.673. so that is the load which i put on one phase of generator or this is total 3 phase load on Generator.......
what parameters are should nessary for control technic dc drive(in rolling mills)?
can a motor acts as a generator
Rotor resistance starter is used to obtain= A increased starting torque B decrease starting current C decrease starting loss D increase efficiency
We have one Energy meter for Measuring the voltage,current,power,energy(KWH,KVARH,KVAH) & power factor.The problem is that the meter does not show whether the PF is lagging or leading.So i want to know that is there any way or calculation to find out that whether the PF sign (lagging or leading) depending upon the above mentioned parameters?