can we use metering current transformer as protection
current transformer if not why? & if yes why?
Answers were Sorted based on User's Feedback
Answer / arun
Selection of CT for protection is majorly depends on the
burden limit and Kneepoint voltage at which the core of the
CT gets saturated,after which it cannot produce the
tripping emf in its core.
So check the burden of CT and kneepoint voltage.
| Is This Answer Correct ? | 19 Yes | 2 No |
Answer / felixraj
the only diff is the knee point voltage
in metering CT this value is very low, because of this
during fault condition the ct get saturated and o/p almost zero
(metering equipments are protected from fault surge)
protection miss leads in metering CT (it may fails or
nuisance tripping)
| Is This Answer Correct ? | 10 Yes | 3 No |
Answer / mohammad
Metering and protection CTs have different accurecy class
level as metering CT has 1 class level and for protection
itis represented by 5P,10P etc..
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / mohsen khoshsefat
Introduction to Protection Transformers
Protective Current Transformers are designed to measure the
actual currents in power systems and to produce
proportional currents in their secondary windings which are
isolated from the main power circuit. These replica
currents are used as inputs to protective relays which will
automatically isolate part of a power circuit In the event
of an abnormal or fault condition therein, yet permit other
parts of the plant to continue in operation.
| Is This Answer Correct ? | 1 Yes | 0 No |
how to maintain ht line?
Why current flows in nutral? As per theory there should be no current in 3 ph explain.
what is FS cable?? Difference between FS and FRLS??
hii.i am a B.TECH(EEE) graduate.i want 2 know wat type of qusns r asked in sbi clerk interview 2 candidates like me??kindly post answers ASAP..
i work as a technician at a private company.. i used to take amp reading for certain appliances such as air con.. the problem is when i clamp the neutral, wire there is a current reading.. from my understanding for single phase system neutral should not have current unless if the circuit is not complete.. yet the air con still work
why 5kW motor becomes unbalance if its relay trip 1st time and its set value is 7.0 A
Excat meaning of burden in only one word?
3 Answers Bhel, DG Electricals,
v=I*R, i.e V is directly proportional to I. now P=V*I. so V=P/I. thus v is inversely proportional to I. so what is the correct one? If both are correct than for which kind of condition this 2 differ
what is pressure relief valve in D.G ?state its function?
for 1000kva transformer how kvar rating is need for this PFI plant. and how does it will calculate? and Apmpere rating of main cable connection?
6 Answers Engineers India, GCC, KP, QPSL, Siemens,
If Dg set load increase 25%, How much increase fuel Consumption (15 kva 2 cylinder DG set)
What are approaches to tackle sedimentation problem of reservoir?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)