How to calculate u.p.s load parsentage plz give me formula
Answer / thangapattu
Befour we should note down the full load of current (rated
current value) Ex-400kva UBS =105A/630a*100
where
105A=currentValue in particular time
630A= Rated Current Value For UBS
= 16% is the percentage load Of UBS
| Is This Answer Correct ? | 4 Yes | 1 No |
Why synchronous motor is used in power factor improvement,dc series in lift
what is eddy current loss?
Why Neutral Busbar CT & transformer neutral CT connected with phase CT in Restricted Earth Fault?
what is the difference between neutral and earth?
What are the no-load losses for the 11000/415V transformer with the following rated capacity? 1.1500 kVA 2. 2000 kVA 3. 2500 kVA 4. 3000 kVA
What is VVVF Drive ?
dear all, i want to ask that what is diversity factor. please explain breifly. because i hve quiet no concept about this.
can transformer develop three phase poer from a single phase source?
In a Circuit how the MCB and Fuse ratings are calculated. And shall the fuse follws the MCB or it is otherwise?
16 Answers Emerson, HCL, Thirumalai Chemicals,
how to calculate bus-bar sizes? (copper bus-bars)
How you calculate the repturing capacity of a HRC fuse
can u tell the difference between star-star transformer and delta to delta transformer.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)