Answer / vinod g
In Restricted earth fault protection Three phase CT is
parralleling (shorting all S1 andshorting all S2 together)
and paralleel conection with Neutral Relay and CT. IN
Healthy conditon current in all the three phase will be
balanced and summation will be zero. During earth fault out
side CT area summation of phase CT currents and Neutral CT
zero, so relay will not pick up. When earth fault inside
the transformer the current in the CT will differ and Relay
will pick and trip the tranformer breaker,so it is clear
that REF is for Transformer Winding protection and Bushing
CT is normally using for phase CT
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / pintu
THIS IS CALLED 5 CT CONFIGURATION (3 PH. CT + 1 X'MER NCT +
1 BB N CT)OF REF PROTECTION. ALL THESE FIVE CTS ARE TO BE
CONNECTED IN PARALLEL. TRANSFORMER NCT SHOULD BE LOCATED
AFTER NEUTRAL BIFERCATION (I.E. PATH TOWARDS EARTH) AS THIS
IS DEDICTAED FOR DETECTING THE RESIDUAL CURRENT IN CASE OF
GROUND FAULT. BUT NEUTRAL BUSBAR CT IS NOT FOR DETECTING
THE FAULT CUURENT BUT FOR THE UNBALANCE CURRENT IN THE
SYSTEM. IT SHOULD NOT BE TRIPPED DURING THE EARTH FAULT.
IN 4 CTS CONFIGURATION OF REF PROTECTION, NEUTRAL BUSBAR CT
CONNECTION WILL NOT BE THERE. YOU SHOULD DECIDE THE 5 OR 4
CT CONFIGURATION AS PER YOUR SYSTEM DESIGN.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / anup mahajan
The purpoae of Restricted earth fault (REF) is to provide
the protection of transformer neutral in case of residual
current. As the fault which lies near phases are known as
external faults and is to be detected by differential
protection but the residual current which is not going to
ground and circulates between neutral and phases are
detedted by REF protection. Please keep in mind that CT
characteristics of this REF must be matched with phase side
CT characteristics.
| Is This Answer Correct ? | 2 Yes | 8 No |
11000volt DG set carnt kaise banvay
Differene between KVA and KW.
in india,we use 230V,50 Hz,whereas many other countries use 110V,60Hz.what r d advs and disadvantages of each of them?
whether a separate starter is used for a motor while it is connected to a vvvf panel?
i am gng to visa interview this july i have 4 backlogs gre 1010,toefl 75,pls give me the tips pls pls
What will happen if we give AC supply to DC motor?
Why USe In -48 DC Volt !
which level of transformer oil has got low dielectric strength ?why?
What if high voltage side circuit breaker of a ehv transformer instead of lvcb? Kindly elaborate.
0 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd,
how much current in live 11 Kv distribution Line?
Why we connect the capacitor in Delta?if we conect in Star what will happen?
why the rating of transformer in k.v.a
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)