what is advantage of using star to delta in place of dol
starter
Answers were Sorted based on User's Feedback
Answer / srilu
decrease starting current by 1/3 times of rated current to
avoid burning of motor during starting
Is This Answer Correct ? | 12 Yes | 1 No |
When the supply voltage is lower than the rated voltage we generally use star delta starter to avoid the over load trip. But in DOL starter, supply rated supply voltage need to start the load
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / liliosa b
it is cheaper compared to other reduced voltage methods
Is This Answer Correct ? | 0 Yes | 1 No |
What are the tests to be done on circuit breaker?
what is the impedence
what is the purpose of using semiconductors in HT cables
What is ignitor and why it is use in Hpmv lamp ?
advantage of using 110v than 230v
What is the problem, if a circuit breaker is not closing.
i am an maintenance engineer. one distribution board have 5 feeder. recently its ELR trips frequently, but it take some times after trip( 10min,20min..)but 3 feeder no load. two feeder only loaded. i checked one feeder IR value all values are above 50Mohm.but B phase to Earth is only 9Mohm.any problem about low value
A genarator is connected through a 20MVA ,13.8/138 KV stepdown transformer to a transmission line. at the reciving end of the line a load is supplied through a step down transformer of 10MVA,138/69 KV rating .A 0.72 PU load evaluated on load side transformer ratings as base values ,is supplied from the above system for system base values of 10 MVA and 69 KV in load circuit the value of the load in generator circuit will be ...........
for testing busbar (33kv) hi-pot .whether we can apply DC r not.and what is the test volt for that .explain
What is dynamo function in DG sets and draw block diagram?
what happen if position of GNA and MNA is changed in machine?
what will happen if we use earthing inplace of neutral for domestic energy meter