how set earth fault over current in relay
Answers were Sorted based on User's Feedback
In any relay Set earth fault to minimum That means If Earth
fault range is 20 to 80 % of secondary current then set it
to 20% . In case of over current calculate rated current
and add 5%for relay & ct error and 5% to over load that
means set it to 110% to full load capacity.
If for 200/1 CT If full load current is 160 that mens 80%
to secondary current of Ct+10% relay CT error and Over load
that means relay ia seted to 180A interms of secondary at
0.9 a that means 90%
Is This Answer Correct ? | 19 Yes | 2 No |
Answer / vijay raskar
When earth fault is occured then relay is set at 2.5 times
than rated current.
Is This Answer Correct ? | 7 Yes | 8 No |
Answer / erharisheee51
we have to connect earth fault relay through current
transformrs , at the neautral side of the generator and
transformers.
Is This Answer Correct ? | 2 Yes | 3 No |
Answer / j.kesavan
POWER CIRCUITE R,Y,B PHASE USING THREE CT ,THIS CT OUT PUT
CONNECT IN OVER CURRENT AND EARTH FAULT RELAY , IF ANY ONE
PHASE TAKE MORE CURRENT OR EARTH FAULT THIS RELAY WILL
TRIP.SETTING THIS RELAY MINIMUM CURRENT,MINIMUM DELAY.
Is This Answer Correct ? | 2 Yes | 5 No |
Answer / motilal sahu
WHEN EARTH FAULT OCCURE HIGH CURRENT FLOW THOUGH LINE.
IF THIS CURRENT IS 10-115 TIMES OF FULL LOAD CURRENT THEN
SHOW THAT EARTH FAULT OCCURE
SO SET THE RELAY FOR 10-15TIME OF FULL LOAD CURRENT
Is This Answer Correct ? | 6 Yes | 10 No |
What is purpose of reactor?.What is different between line and bus reactor?
wat is the need of capacitor on aceiling fan?
How turns ratio test is done in three phase transformers?
10Hp, 3-phase, 415v, 50Hz induction motor. The above motor is to run on Star-Delta connection, so how do i make following hardware selection 1) MCB, 2) Contactor, 3) Wire Gage (Depending on P-P current or Line Current), 4) OLR, Please tell in detail how to do the above, so as to get the ans. of it even if the Hp rating changes.
How to calculate cable sizes in sq.mm. with using motor KW? Any formula there?
18 Answers Aswani Properties, BRB Cable, Construction, Hitachi, L&T, Microcool Systems, Nahar, NWPF, Reliance, Renault, Saha Bright Polytech, SGH, TATA, Techno Electric and Engineering, TFIL, Thermax,
do we need NGR panel when the output of the genset is LV but after that it is step up to 22 kv. condition is 12 genset 400v are operating in parallel.
How much current can carry the 1 sq inch super enamelled copper wire?
1)which height building required lightning arrester? 2)how to calculate the requirement of lightning arrester? 3)what is the pro instrument? 5)how to test protective relay like overload?earth fault relay?
how is efficincy of the transformer is predermined
How to calculate the current carrying capacity of electrical cables
16 Answers Barqaab, Grasim, Havells, HM Cables, Janapriya, Polycab,
what is linear elements
What happen if ac supply is fed to rotor of the alternator?