For what purpose an AVR in generator sensing generator
output voltage?and how the sensing is done by AVR?
Answers were Sorted based on User's Feedback
Answer / dipak062078
AVR is used in the excitation system of the generator.It
senses the voltage changes accross the generator
terminals.Sensing is done PT connected in terminal.According
to the voltage change it increases or decreases the
excitation of the main exciter field and the main exciter
controls the generator field excitation to control the
terminal voltage.
Is This Answer Correct ? | 17 Yes | 2 No |
Answer / indrajeet
AVR (Automatic voltage regulator)has a voltage setting pot
as per requirement say 415 Volts.AVR takes reference of
generator voltage & tries to control as per set voltage by
adjusting excitation voltage.
Is This Answer Correct ? | 1 Yes | 2 No |
Answer / jigs
To regulate the o/p voltage avr senses the gen o/p volt., a
pt is used to step down the gen o/p volt and then it gives
the proper volt signal to avr.
Is This Answer Correct ? | 2 Yes | 5 No |
Why Capacitor & ignator used in MH lamp
ell me capacitor bank chossen formula.load in KW
what is relation between HP & BHP
ii) A shunt motor supplied at 230V, runs at 900 rpm when the current is 30A. The resistance of the armature is 0.4 ohms. Calculate the resistance required in series with the armature to reduce the speed to 600 rpm, assuming that the armature current is then 20A. [12]
what are factors to be consider to design a HT & LT motor?
For high voltage and low current Circuit Breaker preferred is vacuum circuit breaker.why?
what happend when 230v dc motor we supplied a 23v ac supply
2 v/500amp/hr to 1.80vpc at 20 degree celsious 2v/5ooamp/hr to 1.75 vpc at 77degree farren .this is the capacity of a battery .what is the meaning of this . can i get a detailed explenation
When we use PT in HT Panel why the ratio is 11Kv/√3/110v/√3 please explain briefly with suitable formula?
types of transformers?
Define the "All - Day Efficiency" of a Transformer
Why is our voltage always seems to be 3.3Kv,11Kv,66Kvetc.. why not 40Kv,39Kv,65Kv???