For what purpose an AVR in generator sensing generator output voltage?and how the sensing is done ..

Answer / dipak062078

AVR is used in the excitation system of the generator.It
senses the voltage changes accross the generator
terminals.Sensing is done PT connected in terminal.According
to the voltage change it increases or decreases the
excitation of the main exciter field and the main exciter
controls the generator field excitation to control the
terminal voltage.

Is This Answer Correct ?    17 Yes 2 No

For what purpose an AVR in generator sensing generator output voltage?and how the sensing is done ..

Answer / indrajeet

AVR (Automatic voltage regulator)has a voltage setting pot
as per requirement say 415 Volts.AVR takes reference of
generator voltage & tries to control as per set voltage by
adjusting excitation voltage.

Is This Answer Correct ?    1 Yes 2 No

For what purpose an AVR in generator sensing generator output voltage?and how the sensing is done ..

Answer / jigs

To regulate the o/p voltage avr senses the gen o/p volt., a
pt is used to step down the gen o/p volt and then it gives
the proper volt signal to avr.

Is This Answer Correct ?    2 Yes 5 No

Post New Answer

More Electrical Engineering Interview Questions

How to design inductive load for 3 phase 440v and maximum 5 amps for star or delta? Can we use a 15kW, 1450rpm motor for 15kW, 960rpm apllication?If yes.how......n.if thesame motor used what`s it`s sideeefect.

0 Answers  


Synchrounous motor is three phase motor,but its not self starting .why?

23 Answers   Delta Beverages, KI, L&T, NTC, TVS, Wipro,


what is mean by derating factor?

4 Answers   Essar,


what is diffrenance between ACB and Isolator

3 Answers  


why any Elelctricity board insist not to change the buren of their metering CTs or PTs for metering purpose? as a example elect. board not accepted that any customer change their metering CT or PT core burden from 5VA to 15VA.. why?

1 Answers  


Generator protection &generator test

1 Answers  


what is tan delta point in a current transformer?

2 Answers  


1. Why transfomer reting in KVA and Motor in HP

11 Answers   AirIndia, Jindal, Mind Tree,


why two windings are using in single phase AC motor

3 Answers  


why C.T secondary are rated 5A generally?

13 Answers   ABC, Bhel,


WHY EXCITATION OF SYNCHRONOUS MACHINE IS DC NOT AC

8 Answers   NTPC,


How do we calculate conductor size?

1 Answers   Hero Honda,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)