1)Why potential transformer primary site grounded?
2)can be loop between neutral & body for grounding?
3)What is the difference between ELCB &RCCB?
4)Why we use iron core in transformer insted of wooden core?
5)what is the principle of excitation?
6)Why we test the core balance test for transformer?
7)what is creepage?What is the creepage length for
insulators at different voltages?
8)How much type of relays used for differential protection
of generator,transformer & busbar protection?

Answers were Sorted based on User's Feedback



1)Why potential transformer primary site grounded? 2)can be loop between neutral & body for gro..

Answer / neeraj pati

1. Here the HV or LV of THE TRANSFORMER is not concerned.
The star side of the transformer is grounded. i.e the
neutral of the star side is grounded for detecting the
earth fault current in case of earth fault in the protected
zone of the transformer.

2. No the body and the neutral should be grounded
separately . because huge fault current can flow in the
body and other auxilliary protection in case of a earth
fault.

8. Differential protection relays are used. eg ABB
SPAD346C1,c2,c3, Siemens 7ut612 etc .

Is This Answer Correct ?    3 Yes 2 No

1)Why potential transformer primary site grounded? 2)can be loop between neutral & body for gro..

Answer / arb555

1) Usaully relays are connectd in 2ndary . SO to detect faults

2) no

3)ELCB detects phase to earth faults
RCCB - trips if net current is not zero

4) to incresae the permeability
if air used-air core
iron -iron core
no wood- its an insulator
5) Dc fiels required in generators for excitation.

7)I think its the distance b/w insulaotors.

8) Merz pRice circulating current basd relays are common



Better answers always let me know !

Is This Answer Correct ?    2 Yes 1 No

1)Why potential transformer primary site grounded? 2)can be loop between neutral & body for gro..

Answer / manishkalia09

ans not know.
please give me anser of these questions.

Is This Answer Correct ?    3 Yes 3 No

1)Why potential transformer primary site grounded? 2)can be loop between neutral & body for gro..

Answer / abcd

ELCB detects phase to earth faults.It can detect low impedence faults but on the contrary if there occurs a high impedence fault in the system then the fault current may be very small. Such faults are detected by RCCB.

Is This Answer Correct ?    0 Yes 0 No

1)Why potential transformer primary site grounded? 2)can be loop between neutral & body for gro..

Answer / sparta

1. to measure the voltage of the phase we used to ground
the PT ,
2.no
3.

Is This Answer Correct ?    0 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

what is electric current

17 Answers  


why we use the 100% and 95% stator earth fault protection for the synchronus generator ?

0 Answers   Operational Energy Group,


What Normal(Tangent) towers and Tension(Cut-point) Towers?

1 Answers   ABB, BGR Energy, NTPC, Powermec,


can anybody sent me power grid questions. what subject should i prefer for preparation?

0 Answers   Reliance, Vascon,


Dear sir, By which formula u can calculate for a particular kv line there is a range of mw.

0 Answers  






sir i used 3 hp of motor for spraying pump, other home light and other home items which size of allminium pvc wire ix used

0 Answers  


In the Variable Voltage Variable Frequency Drive, how the Voltage and Frequency varied ? Is it varied in the Inverter part of the Drive ? Please give us supporting document if any.

0 Answers  


what is our body resistance value?

11 Answers   Bhel,


How much ampere rating on LT side of distribution transformer and also on HT side of 200KVA transformer

2 Answers   ABB,


if 2 coil of 1000W connect in series and 200 v is applied across it . then what is the total power of coil when coil have only resistive load .

1 Answers   BSNL,


At light load transformer efficiency is less because A secondary output is low B transformer losses are high C fixed loss is high compared to output D copper loss is small

1 Answers  


Why we make earth connection with Transformer Body and What will be the minimum size of copper wire as per code with respect to KVA rating of Transformer?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)