in 3 phase (4 wire) star connection - is current pass through
neutral??
Answers were Sorted based on User's Feedback
Answer / asdf
Only if there are unbalanced conditions between the 3 phase lines.
| Is This Answer Correct ? | 15 Yes | 0 No |
Answer / ankush miglani 9718037333, eba
for star connections if the load is balanced, the phasor
sum of the three currents is zero.
but if the load is unbalanced, the all three phases do not
carry the same load or if there is any fault, a current
passes thru the neutral and the amount is equal to the
current that balances the all three phase currents.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / md. obaydur rahman
We know that,in a star connection for balanced condition the
phasor sum of three line current is zero. As a result in
balanced condition there is no neutral current. But in
unbalanced condition the sum is not zero and a current is
flowed through the neutral wire.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / srikanth
Yes.. current passes through neutral because it is not
balanced load or connection.... due to this current will
pass...
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / theravikumaran
i think, answer is no... but i don't know why
| Is This Answer Correct ? | 6 Yes | 10 No |
What type of bulb used in small size cross symbol boder and original flame type(Deepam)?
HOW MUCH CURRENT DOES SYNCHRONOUS MOTOR TAKES AT SYNCHRONOUS SPEED IN NO LOAD CONDITION ?
What are the limitations of Kirchoff's laws?
If I fill the form of engineering services and I left the exam de to navoidable reasons . Will it counts my one attempt
What are the different types of transformers?
Where r use in Dc motor in power plant?
how to use single phase supply for a three phase equipement.
What is the RMS and DFT principle of analogue maesurments. Which way they are advangages. where which princples give optimum results.
how is the connection of a 3 phase ct trivector meter done on a pole mounted transformer
why generator is design for lagging P.F(power factor)?
reason of capacitor failure or low voltage in alternator wtih 10kva dgset
there are a transformer and a motor. both are connected to 3phase, 415 Volt, 50Hz power supply. Both are working with induction principles. Then, why, motor is rotating and transformer is not rotating.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)