Why transformer called by KVA?..

Answer / fahad

bcoz the power factor of load is not known during the
manufacturing, this is also done during load calculation.
For reference you can see a indian book " B.L Theraja -
Electrical Technology" ....

Is This Answer Correct ?    7 Yes 2 No

Why transformer called by KVA?..

Answer / amit

bcoz iron losses depdens on voltage and copper losses
depends on current that's why transformer rated in KVA

Is This Answer Correct ?    7 Yes 3 No

Why transformer called by KVA?..

Answer / thanigai1984

Transformer is not consider the power factor so its
capacity is in KVA

Is This Answer Correct ?    7 Yes 7 No

Why transformer called by KVA?..

Answer / mathivanan k

the pf will be indipendent to the trf,the pf only act at
load equipment side only
so the trf is not load
and it's losses depending copper&coreloss then only it is
mention in VA it is bulk amount so KVA

Is This Answer Correct ?    1 Yes 1 No

Why transformer called by KVA?..

Answer / mintu kr. pandit

Mainly reason for no-load current consumption of transformer in losses hysteresis loss and eddy current loss.

Is This Answer Correct ?    0 Yes 1 No

Why transformer called by KVA?..

Answer / realas

Because the flowing of current in secondary winding is
without/no losses so the apparent power is zero. Hence, the
transformer may call either by KVA or KW since it is equal.

Is This Answer Correct ?    0 Yes 3 No

Why transformer called by KVA?..

Answer / sachin verma

BECAUSE VOLATGE IS measured in volts and current in ampere.

Is This Answer Correct ?    2 Yes 8 No

Why transformer called by KVA?..

Answer / ravindranath

transformer of is close to one that is why it is not expressed in kw

Is This Answer Correct ?    0 Yes 8 No

Post New Answer

More Electrical Engineering Interview Questions

What is Ton Capacity of Air Conditioner?

1 Answers   TATA,


Why nutral wir used thinner than phase wire

3 Answers  


why the NGR (neutral grounding resistor) always OFF during DG off?

0 Answers   Bhel,


What is load curve?

2 Answers  


what happenes if two voltage source connected in parallel will be connected to load.

3 Answers   Efftronics Systems,






How can you measure battery AH?

1 Answers  


why permanent magnet generator have higher frequency of 400hz

3 Answers   Jaypee,


Why should we use Star-Delta connection in step down power transformers?

7 Answers   L&T,


There are two nos of 33Kv/11Kv 5MVA transformers conecting through HT cable from substation having metering at substation itself.One transformer used at a time another remains stand by.Further 11 nos of 11Kv/440V transformers are attached on it and each transformer is having its own Power factor correction panel.Now one 33/11Kv transformer at no load condition/Stand by condition is having power factor in leading side upto 0.21 and while when another tranformer at same situation have power factor in lagging 0.42. Now one thing is clear that transformer one is having 1.5 Km long 33kv cable due to that PF goes in leading side and another is having only 250 mtr length remains him lagging. Now i want to know that how i can maintain the Power factor at no load/ stand by position though both are behaving in seperate manner.

1 Answers  


What are the voltage values for LT,HT,EHT and other voltages??

22 Answers   INEL, MNC,


what are the disadvantages of low power factor

0 Answers   HMK,


what is the criteria for selecting fuse rating in 1phase, 2phase & 3phase welding sets?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)