When we are working on transformer(132\11KV). we are going
to isolate the transformer from both HV side and LV side.
then we are applying grounding on both side. My question is
that we required to isolate the VT which is still connected
from secondary side.?
Answer / binod
YES ,IT IS REQUIRED TO ISOLATE LINE VT IN SECONDARY
SIDE,BEACUSE BEFORE CHARGING THE TR. WE MUST MEASURE THE
INSULATION VALUE BY MEGGER
INSULATION VALUE TAKEN IN FOLLOWING MANNER
1)PH(HV)TO EARTH(EARTH CONNECTION REMOVED FROM TR. EARTH
BUSHING)
2)PH(LV)TO EARTH(IN THIS TEST THE LINE PT ISOLATED FROM THE
CIRCUIT OF LV SIDE OTHERWISE THE VALUE IS ZERO)
3)PH(PRIMARY)TO PH(SECONDARY)
4)CONTINUTY TEST BETWEEN PHASES OF LV(R Y B)&HV(RYB)
| Is This Answer Correct ? | 1 Yes | 0 No |
how to calculation increase power factor for single phase
how hazordious area is classified at an oil & gas plant and categorise suitable class of electric equipment in that area like induction motors, LCS, Lighting Fixtures Fluerescent/Flood lights Mercury& sodium lights, J.Bs, Power Cables etc
Discuss about gear cutting machines.
what is power factor in ac ckt ?
What is SF6 Circuit Breaker?
Can any horizontally mounted motor be used as vertical?
What is the advantage and disadvantage of dry type transformer?
why two wires are wound alternately to each other in single phase wires?
what is IP55,IP65
why single core HT cable need only one side earthing?
what is lumped and distributed elements?
Why we can not get 100% efficiency from a Gas Generator?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)