Please any one can explain how to calibrate transmitter
(smart) online with out remove from the container suppose
it is interface level or static pressure level measurement
we dont want to remove transmitter from the container mean
it is running plant please give me detail. thankx brothers
Answer / jazz
Use a smart communicator device such as HART
calibrator/communicator. Connect it across +/- terminals,
whether in the instrument, junction box, marshalling, or
system cabinet, then initiate communication with the smart
transmitter. If you calibrate on-line, the HART communicator
will ask you to put device in manual, and advise control
room that you are calibrating the HART transmitter. Using
the HART communicator use loop/calibrate function and
simulate, 4,12,20 mA corresponding to 0%,50%, 100% of level
or pressure.
Is This Answer Correct ? | 6 Yes | 6 No |