While connecting the flood light plug on to the 415 V
distribution panel,there was spark and the cable got burnt.
Three ignitors of the flood light also burnt of. The lamps
are of 400 W (total 6 lamps) connected through 1.5 mm2
cable. The plug was immediately removed from the circuit.
There was a 30 mA RCD connected and a 250 A MCCB; however
both did not trip. What could be the possible reasons for
the circuit devices not to trip?Can someone assist please.
Additional info if needed can be provided.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
It appears that you have connected a phase instead of neutral.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / albaloshi4u
check flood light another distribution box whether your flood light is working properly or faulty and also check your db phase voltage.
| Is This Answer Correct ? | 0 Yes | 0 No |
What is the minimum setting in REF relay because i am facing some problem whenever power resumes after power failure my transformer is tripping because of REF trip. I am using CSPC make numerical relay(DIP switches). Now setting is 15 percentage. What is the reason for this triping. I sm waiting for answer
Why 1500 rpm of deasel generator please explain to me?
1 Answers Integral BioSciences,
what is the meaning of x,m,k in the relays?
What are the causes ,revers rotation of a kwh meter?
PLEASE SEND ME NTPC RELATED INFORMATION LIKE WHICH TOPICS HAV MORE SCOPE,BOOKS TO READ,CUT OFF...PLEASE.mail at thiru.1203@gmail.com
which protection are used for turbo generator in thermal power plant.
What type of changeover switch needed to run a load of five 1.5 tonn ACs.
can we use breather in a SEALED power or distribution transfomer instead of injecting nitrogen.
What are the types of feedback oscillators?
Electrical breakdown strength of an insulating material depends on............?why because?
IN OLTC we observed "OUT OF STEP" Alarm, we have two different transformer, when both are in parallel this type of alarm observed. what's the meaning of this alarm and why it occurs???
what is motor capacity of 80TR chiller? and also say what is the formula related temperature, motor capacity, TR?
0 Answers Apotex, Periyar Chemicals,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)