While connecting the flood light plug on to the 415 V
distribution panel,there was spark and the cable got burnt.
Three ignitors of the flood light also burnt of. The lamps
are of 400 W (total 6 lamps) connected through 1.5 mm2
cable. The plug was immediately removed from the circuit.
There was a 30 mA RCD connected and a 250 A MCCB; however
both did not trip. What could be the possible reasons for
the circuit devices not to trip?Can someone assist please.
Additional info if needed can be provided.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
It appears that you have connected a phase instead of neutral.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / albaloshi4u
check flood light another distribution box whether your flood light is working properly or faulty and also check your db phase voltage.
| Is This Answer Correct ? | 0 Yes | 0 No |
In any Industry, Which voltage level either 3.3kV or 6.6KV to be chosen? Then I would like to know ,Is there any cost consideration or Rating of motor?
Which type of transformer is used for lighting loads?
why we measure ouput of transformers in kva.
In an electrical power supply,why if neutral phase of a 3phase supply fail over current occur but if it's single phase supply neutral phase fail low current occur?
Will it be OK to connect a 5MVA 33/6.6kV Ynd11 Transformer to a Star connected Motor. Or on other words connecting a Delta to a Star. I have another 30MVA 33/11 Dyn11 and would it be practical to convert it to Dd0 consequently converting the Voltage Ratio to 33/6.35kV Dd0.
What is Horan Gap Fuse? Where it is used?
what is the generator rating for 40 amp load of 3phase motor.?? 400v voltage of generator... plz tell me with formula its urgent...plzzz... and also tell me that this 40 amp at all phases mean 40 amp on red,40 amp on yellow,40 amp on blue...... or the total sum of that 3phase is 40 amp....
how to Select its CORE in electrical cables based on its applications? or Application of various types of electrical cable based on it CORE?
If the generator will trip, what you will do as an electrical technician in charge.
List examples of current sources?
What type of surgery impedence with 200ohs
Explain the function of VFD
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)