What will be the size of cable required for 5.5 KW motor (
Full load current 10 Amps approx.), Starting current with
DOL is 120 Amps. Aprrox. Short circuit current with LLLG
fault is 2000 Amps Approx.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
6 sq mm copper cable and 10 sq mm if the usage is
non-stop.cables can withstand heavy currents for short periods.
| Is This Answer Correct ? | 17 Yes | 3 No |
Answer / birinchi87
4 sq. mm is sufficient. In our plant we are using 2.5 sq. mm for 5.5 KW and 4 sq. mm for 11 KW.
| Is This Answer Correct ? | 18 Yes | 11 No |
What will be the full load current of 60KVA UPS. Suggest for this formula.
Which Motor used in Fan's Motor ?
3 Answers Matsui Technologies,
how is differential relay working in transformer.comparison with generator defferntial relay
how to set relay setting? and example calculation...
explain the mode of metal iranafer in Co,welding
Why is the earth socket in an electrical plug outlet made thicker and lenghty?
what is the difference between a hooter and a mcp
is it possible to start a motor in felid connected to a remote mcc
which type of starter is suitable for single phase motor ?
what are the advantages and disadvantages of speed control of 3 phase induction motor by varying frequency explain with drawing
How can calculate thermal overload in relay?
Block diagram of Power line communication?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)