What will be the size of cable required for 5.5 KW motor (
Full load current 10 Amps approx.), Starting current with
DOL is 120 Amps. Aprrox. Short circuit current with LLLG
fault is 2000 Amps Approx.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
6 sq mm copper cable and 10 sq mm if the usage is
non-stop.cables can withstand heavy currents for short periods.
| Is This Answer Correct ? | 17 Yes | 3 No |
Answer / birinchi87
4 sq. mm is sufficient. In our plant we are using 2.5 sq. mm for 5.5 KW and 4 sq. mm for 11 KW.
| Is This Answer Correct ? | 18 Yes | 11 No |
5.WHICH TYPE WELDING PROCESSES USES NON CONSUMABLE ELECTRODE.........
about transformer oil material & Test name for the measurement of its dielectric strength & wht will u do if its dielectric strength goes low ?
how to work droop ct in generating station
why are installed water leakage detection system data centers & server rooms
Why CT secondary should not be kept open?
what is relation between torque and speed / rpm?
how braking & making capacity of circuit breaker are calculated?
why are distributed windings generally used in alternators?
what is the method of electric earth for the protection of low voltage electric equipment
1 Answers MacLellan, Shiva Corporation, Siemens,
What is the meaning of GRID?
What is thyristor?
Difference between MCC and PDB
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)