What will be the size of cable required for 5.5 KW motor (
Full load current 10 Amps approx.), Starting current with
DOL is 120 Amps. Aprrox. Short circuit current with LLLG
fault is 2000 Amps Approx.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
6 sq mm copper cable and 10 sq mm if the usage is
non-stop.cables can withstand heavy currents for short periods.
| Is This Answer Correct ? | 17 Yes | 3 No |
Answer / birinchi87
4 sq. mm is sufficient. In our plant we are using 2.5 sq. mm for 5.5 KW and 4 sq. mm for 11 KW.
| Is This Answer Correct ? | 18 Yes | 11 No |
What is the difference between earth fault and restricted earth fault protection?
What current can be carried by 25 sqmm copper cable safely?
what is fundamental difference between voltage and current
How to reduce the static electricity producing in solvent room? By P.D.Patil BioCon
why does voltage generation at 11 kv?
IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoing breaker kA rating to be equal to busbar kA rating?
How the size of transformer decreases if we increases the frequency?
what is diff b/w electrical & electronics ?
What is the Efficiency in Electric motor ?
What does the term supermesh means?
what type of relay has to be used for tripping the circuit from mains when a fault occur in a machine
i am completed in B.E(Electrical and Electronics Engineering) with 8 months experience in Quality Control Engineer at Bharathi Industries,Coimbatore.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)