How can we reduce the reactive power consumption of your
12.5 MVA power transformer.
Answers were Sorted based on User's Feedback
Answer / manish yadav
basically reactive power consumption is depend upon the
load pf.. as Q=kw*sin@ ...n so make an arrangement such
that capacitor is connected across the secondary while load
is on n get separated at low load ..or no load
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / balaji
To reduces reactive power consumtion we need to connect a
capacitor bank which absorbe R-KVAR...
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / yano
reduce inductive loads such as motors anyway bank capacitors
may help to reduce the KVR
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / suburavichandran
add a power factor correcting capacitor to all the loads you are using.. now most of the loads are provided with such an arrangement. hence you can minimize the reactive power consumption
Is This Answer Correct ? | 0 Yes | 1 No |
what does the regenerative braking mean?and how it used for Dc motor? thanks.
What is the diffrence between PS & metering CT (5p20,0.5 etc.)? Why in PS class CT only Vk is given ? Is PS class CT is more accurate than metering CT?
Why frequency changes due to load variation in power system ? i.e why when load increases frequency decreases?
what is allowed value of zero sequence impedancce of 6.6 kv nuetral earthing transformer ?what is the actual value
what are the types of cables?
How many types of losses occur in a transformer?
What is your acheivements
What is the function of an exciter in a generator?
Why 30kw 40 hp 4 pole 3ph induction motor over heated?any steps on reduction in heat?
how we can calculate the transformer size.
21 Answers Avalon, Edison, Hyundai,
At site, we have 30Kw motor (3 phase, 400V,50Hz) and FLC 54A as per the nameplate. At the time of starting it draws 840A instead of 390A (7.2%). As per the data sheet also its 390A starting current. it thru a dol starter from the MCC. can anyone tell what is the problem in the motor
what is the size of ht cable of 33kv ht line and transformers ratings are 2.5mva and 5.5mva.please send formula also.