In a Tap changing transformer where is the tap connected ,
is it connected in the primary side or it is connected in
secondary side
Answers were Sorted based on User's Feedback
Answer / suryaraj
Tapings are
connected to high
voltage winding
side, because of
low current. If we
connect tappings to
low voltage side,
sparks will produce
while tap changing
operation due to
high current. Not
depend on primary
or secondary.
| Is This Answer Correct ? | 39 Yes | 0 No |
Answer / ronak panchal
tap changer is connected at ht side.
its not depend on primary or secondary winding but where the
ht side and lt side is been defined.
if primary winding is ht and secondary winding is lt then
tap changer will be at primary.
| Is This Answer Correct ? | 18 Yes | 2 No |
Tap Changer is always installed at HT side,since at HT side
current is low .
reasons for not installation at LT side
1.high current
2.when we have to change the tap there is little bit
sparking, and sparking cause gas production ,thus buchhloz
relay operate.
| Is This Answer Correct ? | 10 Yes | 0 No |
Tap changing are always provided in HV SIDE OF TRANSFORMERS
AS CURRENT IS LOW.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / vishnu vardhan singh thakur
its on secondary side. if it is placed on primary side and
when the voltage is increased magnetic core will be saturated
and if the voltage is reduced the magnetic core is not fully
used...... and mostly tappings are provided on HV side because
the current on HV side is less where it is high on LT side. so
when short circuit occurs no damage will happen thats y
tappins are provided on HT side
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / deepak verma
actually we take o/p always at secondary side and tapping is used to adjust the o/p voltage, so tapping is done always at sec. side
| Is This Answer Correct ? | 2 Yes | 8 No |
What is meant by Creepage Distance in Insulators?
While HT line put on to activate ACB in low tention panel VCB tripping instantly.why it happens
why transformer impedance measure in % (percentage)
what are the parameters plays a major role in Potential transformer Burden calculation??
How to identify the whether its an isolator or Breaker in MDB
for hipot test on 33kV busbar, we will test on 70 kV or 56kV, what is the acceptable leackage current?
Why have to use copper cable for local isolator to motor ?
i need project topics along with circuit diagram in the electrical and electronics engg and also some websites regarding projets.
What are the temperature elements?
What can make the the overloads operate when a star delta three phase motor starts?
why we remove capacitor connection in 3 ph Induction Motor while taking noload test.
What is difference between earth leakage relay and restricted earth fault relay ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)