Answer / suryaraj
Tapings are
connected to high
voltage winding
side, because of
low current. If we
connect tappings to
low voltage side,
sparks will produce
while tap changing
operation due to
high current. Not
depend on primary
or secondary.
| Is This Answer Correct ? | 39 Yes | 0 No |
Answer / ronak panchal
tap changer is connected at ht side.
its not depend on primary or secondary winding but where the
ht side and lt side is been defined.
if primary winding is ht and secondary winding is lt then
tap changer will be at primary.
| Is This Answer Correct ? | 18 Yes | 2 No |
Tap Changer is always installed at HT side,since at HT side
current is low .
reasons for not installation at LT side
1.high current
2.when we have to change the tap there is little bit
sparking, and sparking cause gas production ,thus buchhloz
relay operate.
| Is This Answer Correct ? | 10 Yes | 0 No |
Tap changing are always provided in HV SIDE OF TRANSFORMERS
AS CURRENT IS LOW.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / vishnu vardhan singh thakur
its on secondary side. if it is placed on primary side and
when the voltage is increased magnetic core will be saturated
and if the voltage is reduced the magnetic core is not fully
used...... and mostly tappings are provided on HV side because
the current on HV side is less where it is high on LT side. so
when short circuit occurs no damage will happen thats y
tappins are provided on HT side
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / deepak verma
actually we take o/p always at secondary side and tapping is used to adjust the o/p voltage, so tapping is done always at sec. side
| Is This Answer Correct ? | 2 Yes | 8 No |
In Railway,why we are used HT Line 25KV ?.why we are not used 11KV,33KV and others for This?
37 Answers Airtel, BSNL, RRB,
HOW TO SELECT THE COPPER CABLE SIZES OF MOTORS,TRANSFORMERS?
It is used or not HT cable single core 630 sqmm in LT 3 phase capacitor bank which is used in PCC(power control center).
3phase cable calculation formula by motor load
what are factors comes under relay setting (distance relay 7sa52) under OPEN DELTA VTs connection??
Neutral to earth and phase to earth voltage how much.
what is the difference b/w neutral and earth?what is the need of earthing and what are the different methods for earthing?
What is the drawback of class b amplifier? How is this minimized?
A genarator is connected through a 20MVA ,13.8/138 KV stepdown transformer to a transmission line. at the reciving end of the line a load is supplied through a step down transformer of 10MVA,138/69 KV rating .A 0.72 PU load evaluated on load side transformer ratings as base values ,is supplied from the above system for system base values of 10 MVA and 69 KV in load circuit the value of the load in generator circuit will be ...........
How will polarity test of Dy5 Transformer ?
what is different between earthing and grounding for a electrical eqipment ?
2 Answers BARC, Omega Maritime,
what are the applications of transistors with low dc gain, high dc gain and medium dc gain( beta)?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)