how can we decide where we have to DYn11 or other vector
group transformer
Answers were Sorted based on User's Feedback
Answer / ramachandran n
Vector Groups are the IEC method of categorizing the
primary and secondary winding configurations of 3-phase
transformers. Windings can be connected as delta, star
(wye), or interconnected-star (zig-zag). Winding polarity
is also important, since reversing the connections across a
set of windings affects the phase-shift between primary and
secondary. Vector groups identify the winding connections
and polarities of the primary and secondary. From a vector
group one can determine the phase-shift between primary and
secondary.
The first criterion to consider in choosing a vector group
for a distribution transformer for a facility is to know
whether you want a delta-star or star-star. Utilities often
prefer star-star transformers, but these require 4-wire
input feeders and 4-wire output feeders (i.e. incoming and
outgoing neutral conductors). For distribution transformers
within a facility, often delta-star are chosen because
these transformers do not require 4-wire input; a 3-wire
primary feeder circuit suffices to supply a 4-wire
secondary circuit. That's because any zero sequence current
required by the secondary to supply earth faults or
unbalanced loads is supplied by the delta primary winding,
and is not required from the upstream power source. The
method of earthing on the secondary is independent of the
primary for delta-star transformers.
The second criterion to consider is what phase-shift you
want between primary and secondary. For example, Dy11 and
Dy5 transformers are both delta-star. If you don't care
about the phase-shift, then either transformer will do the
job. Phase-shift is important when you are paralleling
sources - you want the phase-shifts of the sources to be
identical. If you are paralleling transformers, then you
want them to have the same the same vector group.
If you are replacing a transformer, use the same vector
group for the new transformer, otherwise the existing VTs
and CTs used for protection and metering will not work
properly.
Is This Answer Correct ? | 40 Yes | 7 No |
Answer / gunasekaran
normally Dyn11 vector group using at distribution
system.because GT are YNd1 for neutralizing the load angle
between 11 and 1. we use Dyn1 at distribution system we r
using GT are YNd11. in some industries 6 pulse electric
drives are using due to this 5thharmonics will generate if
we use Dyn1 it will be suppress the 5th harmonics.
Is This Answer Correct ? | 10 Yes | 12 No |
Answer / praween
Generally Vector group is configure the tranformer primary and seccodry winding with each other....these vector group are diffrent type like as dyn1,dyn11 ,dyn0,dyn6 .we understand the phase difference with niddle of clock..there are30 degree make between two..that means of dyn11 is delta winding laggs 30 degree from star winding of transformer....
Is This Answer Correct ? | 0 Yes | 4 No |
Answer / eng. ahsan rassam
DEPENDING ON TYPE SYSTEM VOLTAGE FOR EXAMPLE IF WE HAVE
33KV AND 11KV WE CHOOSE VECTR GROUP DYN11. AND IF WE WANT
TO OPRET TWO OR MORE TRANSFORMER OR GENERATOR IN PRALLER WE
MUST CHOSSE SAME VECTOR GROP.
Is This Answer Correct ? | 6 Yes | 18 No |
What is the kva?
2 Answers Makino Auto, SAL Steel Power, Sapphire Group,
why we dont prefer ac voltage controller instead dimmerstat [if both have same rating] for conducting experiments in laboratories?
What is the maximum percentage voltage drop (vd%)for a motor control center
what is differant beetween overload current and phase current?
A simple Question from all.... If Voltage drops then its rated value what will be effect on a Residential load? similarly if voltage rises from its rated value then what will be effects on a load? i know if voltage drops the equipment or device draws more current then its rated what are other reasons ? thanks in advance for ur time.......
when turbine trips generator will becomes induction motor or synchronous motor?
What are the protections to be used for Generator?
How single phase & 3 phase motor select rotating direction ie clockwise/anticlockwise
why r we using vaccuum circuit breakers in the place of m.o.c.b.
The current though a branch in a linear network is 2A when the input voltage is 10 volts. If the voltage is reduced to 1 volt, and the polarity is reversed, what is the current flowing through the branch ?
design of IGBT firing circuit for 11KV
why it is mentioned as 8/10 mva transformer why not directly 8mva or 10mva transformer. please explain me the full detailed reason.