how can we decide where we have to DYn11 or other vector
group transformer
Answers were Sorted based on User's Feedback
Answer / ramachandran n
Vector Groups are the IEC method of categorizing the
primary and secondary winding configurations of 3-phase
transformers. Windings can be connected as delta, star
(wye), or interconnected-star (zig-zag). Winding polarity
is also important, since reversing the connections across a
set of windings affects the phase-shift between primary and
secondary. Vector groups identify the winding connections
and polarities of the primary and secondary. From a vector
group one can determine the phase-shift between primary and
secondary.
The first criterion to consider in choosing a vector group
for a distribution transformer for a facility is to know
whether you want a delta-star or star-star. Utilities often
prefer star-star transformers, but these require 4-wire
input feeders and 4-wire output feeders (i.e. incoming and
outgoing neutral conductors). For distribution transformers
within a facility, often delta-star are chosen because
these transformers do not require 4-wire input; a 3-wire
primary feeder circuit suffices to supply a 4-wire
secondary circuit. That's because any zero sequence current
required by the secondary to supply earth faults or
unbalanced loads is supplied by the delta primary winding,
and is not required from the upstream power source. The
method of earthing on the secondary is independent of the
primary for delta-star transformers.
The second criterion to consider is what phase-shift you
want between primary and secondary. For example, Dy11 and
Dy5 transformers are both delta-star. If you don't care
about the phase-shift, then either transformer will do the
job. Phase-shift is important when you are paralleling
sources - you want the phase-shifts of the sources to be
identical. If you are paralleling transformers, then you
want them to have the same the same vector group.
If you are replacing a transformer, use the same vector
group for the new transformer, otherwise the existing VTs
and CTs used for protection and metering will not work
properly.
Is This Answer Correct ? | 40 Yes | 7 No |
Answer / gunasekaran
normally Dyn11 vector group using at distribution
system.because GT are YNd1 for neutralizing the load angle
between 11 and 1. we use Dyn1 at distribution system we r
using GT are YNd11. in some industries 6 pulse electric
drives are using due to this 5thharmonics will generate if
we use Dyn1 it will be suppress the 5th harmonics.
Is This Answer Correct ? | 10 Yes | 12 No |
Answer / praween
Generally Vector group is configure the tranformer primary and seccodry winding with each other....these vector group are diffrent type like as dyn1,dyn11 ,dyn0,dyn6 .we understand the phase difference with niddle of clock..there are30 degree make between two..that means of dyn11 is delta winding laggs 30 degree from star winding of transformer....
Is This Answer Correct ? | 0 Yes | 4 No |
Answer / eng. ahsan rassam
DEPENDING ON TYPE SYSTEM VOLTAGE FOR EXAMPLE IF WE HAVE
33KV AND 11KV WE CHOOSE VECTR GROUP DYN11. AND IF WE WANT
TO OPRET TWO OR MORE TRANSFORMER OR GENERATOR IN PRALLER WE
MUST CHOSSE SAME VECTOR GROP.
Is This Answer Correct ? | 6 Yes | 18 No |
if power factor comes in leading & showing -0.95. Is there any effect on electrical system? if yes, then please tell me what would be the effects. & how long we keep power factor in leading. Keeping power factor in leading shows more KW & less KVA is it correct or not.
what is the advantage of connecting capacitors in delta than in star?
when a three phase motor in running condition consumes 2A in each phase,and if one of the phase gets fails what will be the consumption in other two phases
Why Earth pits are inter connected
what will happen if i will done heart shape hole in transformer core?
what is the rating of a power transformer?
What is the correct procedure to shutdown VCB in 11kv substation.safety and work procedure
why we use 20 KV, 10KA LA on 22 KV Line
How to know the back up time for a 5KVA UPS which is connected to 15 nos. of computers? Is there any formula for this? pls. tell me.
What are documents to be required for export of the material?
Why transformer neutral earthing? What is advantages?
how can i determine the KVA/MVA rating of transformer precisely?? is there any standard test?????