How to calibrate a orifice differential pressure flow
transmitter in process?
Answer / ayaz
first communicate ccr tag conform and turn MOS if required
when 5 way manifold
1 hp side close
2 equalizer open
3 lp side close
and then hp and lp drain or vent should be open
the transmitter will show zero if not calibrate it
first adjust the zero
2nd second span check and adjust
and then service
1 drain or vent close
2 equalizer close
3 and then hp side open and lp side open
| Is This Answer Correct ? | 3 Yes | 0 No |
My rtd working well at the same time r/i converter is not working properly.when power is given to rtd..it is giving 30mA and getting 2.4 mA if i remove the compensate leads No matter how many ohms.why it is happening like so?what is the solution?rtd range-0-200deg c& 4-20 mA o/p.please give me solutiin anyone......
In RTU Panel we are having several Analogue & Digital Inputs /Outputs. We are recently facing some problems over Analog inputs , which are not updating properly (But Digital Input are updating normally) Can any one tell me from where the problem is creating , we have checked PLC CPU card, Analog Input card & we reconfigured ,But still the issue is there. Issue : 1. Sometimes Analog values are updating & sometimes not. 2. Analog values are not updating normally , showing some wrong Values 3. Total dead (0 value) Analog values are Level & flow measurement from the field instruments. (But in field the instruments are working normally & Displaying the values normally in local display unit) This problem we are facing in our Water Plant. If any one experienced this same problem or having any ideas related to our issue PLS send your valuable Answers/Replies...
What kind of feedback is used in DP cells.
dear sir we have insatlled positioner model no.sipart PS2 make Siemens at our control valves . now problem is if we want to increase the response of valve opening speedy /fast. what parameters do we change for positioner ? any idea. please guide us.
If hart communicator provide 4-20ma source to any transmitter during the callibration?
what is all types of analyzer in water production plant?
How can I zero check of wet leg type DP Tx ?
in the boiler in the main steam line and its bypass line and the startup vent vales are only motorised valves why cant we use other types of valves such as pneumatic.
Can please tell mi about SIOS, PRM, SERVER, and what is the diference between PIN LAN, PCS LAN,APC Server, and please send the Doc if possible for referance,mail id patil_amit17@yahoo.com
without a positionar can a control valve operate? give the difference of operating with positionar and without positionar?
1. what is modbus cable? 2. what kind of communication we are using for the interface of DCS, ESD and Third party cabinets? 3. What is serial communication and peer to peer communication?
What is the reason for not giving very High Proportional Gain Kp in PID Controller?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)