How to calibrate a orifice differential pressure flow
transmitter in process?
Answer / ayaz
first communicate ccr tag conform and turn MOS if required
when 5 way manifold
1 hp side close
2 equalizer open
3 lp side close
and then hp and lp drain or vent should be open
the transmitter will show zero if not calibrate it
first adjust the zero
2nd second span check and adjust
and then service
1 drain or vent close
2 equalizer close
3 and then hp side open and lp side open
Is This Answer Correct ? | 3 Yes | 0 No |
what is the control valve?how many types of control valves are there
6 Answers Chemin, Hindustan Zinc,
Can anybody explain what is the different between ESD & PLC
HOW FOREIGN CONTROL SYSTEM CAN BE CONNECTED WITH DCS?
How oil line flow measured?eplain about instruments used and working principle?
EXPLAIN SOME IMP QUESTIONS AND ANSWERS ON TOPIC ELECTRONICS,INSTRUMENTATION.........
why pneumatic control signal output is use 0.2 to 1 kg/cm2
How to connect another 24 volt dc power supply in circuit when previous power supply has become weak.what is the connection?
2 Answers Bhole Baba Dairy Industries,
in plc source and sink meaning?
can u guys tell me why we are using sheild in junction bos wiring ~! ?
What are the charcterstics of a P&ID controller block for Governor speed raise or lower for a load sharing functionality between 4 Gas turbines in droop mode.
I have a orifice installed in plant which is design for 0~100 inH2O for 0~80MMSCFD, now due to process change the maximum flow is change to 120 MMSCFD so for this new process value what will be the DP across orifice.
what is o2 analyzer and how it measured ,what is the role of this analyzer in cfbc boiler...