Wtat is mean by GHOAST VOLTAGE?
Answers were Sorted based on User's Feedback
Stray or ghost voltages occur from capacitive coupling,
which takes place between energized circuits and non-
energized non-connected adjacent wiring.
practical occurance : When facilities or buildings are
built and wired, it's very common for the electricians to
pull extra wire thru the conduit for future use. These
wires are typically left unconnected until needed.at this
situation coupling effect takes place as explained above.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / anoop
Ghost voltage is the voltage which is occurred due to the
long length of cable (upto 400 mtrs) which generates
induction in the cable. Suppose we use a 16 c X 2.5 Sqmm
cable at a distance of 430 mtrs there will a induction in
ideal cores of cable due to long length of cable. Which is
called the ghost voltage.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / heena
it use to calculate net electric field as well as potential..
Is This Answer Correct ? | 0 Yes | 3 No |
Why current shoots up in the secondary on the knee point voltage during saturation test of CT? How core saturation effects the secondary current (while the primary side is open)? What the logic behind this?
explain transformer ct connection?
Earth leakage relay basic knowledge principle
what is the minimum bdv value for 400 kva transformer?
Installation method of self treated earth electrode.
We have drive feeding an output contactor for a 5000 hp motor @ 5kV application. The motor FLA is 629amps x 1.25% service factor = 786.25 amps The cable that we current have in place between the drive and the output contactor is 350kcmil- MV-105 (parallel cables). Per the NEC table 310.60 (C) (69). This show the cable ampacity is at 615 amps per cable for a rating of 1230 amps. We have derated the cable for the cable tray and the multiple cables application and our calculations show that after the correction factor factor we are at 922amps. 1230 amps x .75% correction factor factor = 922.5 amps. The customer is driving us to then use another safety factor of .25% off of the already derated cable. Can you please provide a longhand calculation for your solution on this application?
state application of relay in transmission line?
What is an Air COmpressor
the single phase voltage is 230 volts and threee phase is 430 v.why three phase is not 660 v?
if AVR fails in alternator. what will be the effect.
Rated moter voltage and frequency is 380volt 60 hz but moter is running at 380votac 50hz is this harmful for moter winding
which is the best institute for PLC,SCADA,DCS in hyderabad