Answer / nishad
for the protection of generator we useing
1, under voltage/ overvoltage Relay
2Under/over frequency,
3, Reverse power relay,
4, Earth fault Relay
5, Differential Protection relay
6, over load protection
8, resticted earth fault relay ***(optional)
9,RTD's for bearing & winding >> protect from over heat
10,if it contain in clossed container provide differential
pressure relay,
These are the normal protection from Electrical side.
| Is This Answer Correct ? | 14 Yes | 0 No |
The following are the main protection schemes adopted for
our generator.
1. Generator Differential Protection
2. Generator & Transformer Differential Protection
3. Loss of Field or Loss of Excitation Protection
4. Negative Sequence or Current Unbalance Protection
5. Over Fluxing or Over Excitation Protection
6. Over Current Protection
7. Stator Earth Fault Protection
8. Rotor Earth Fault Protection (64R)
9. Restricted Earth Fault Protection
10. Backup Impedance Protection
11. Low Forward Power Protection
12. Reverse Power Protection
13. Pole Slip Protection
14. Pole Discrepancy Protection
15. Local Breaker Back Protection
16. Bus Bar Protection
17. Over Frequency Protection
18. Under Frequency Protection
19. Over Voltage Protection
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / renjith v.r
The following are to be used
1.Voltage restraint O/C relay
2. E/F relay
3. stand by E/F relay using CT in neutral earthing conductor
4. Under voltage ,over voltage relay
5. Differential potential relay
6.negative sequence relay
7.Vector surge relay
8.Reverse power and Reverse reactive power relay
9.rotor E/F relay
9.High vibration, oil temperature, Overspeeed and under speed alarm trip
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vedprakash uppadhaya
reactors, thyristor contoroled rectifier
| Is This Answer Correct ? | 2 Yes | 3 No |
what is the earth to neutral voltage(maximum and minimum) according to ieee standards
can we use breather in a SEALED power or distribution transfomer instead of injecting nitrogen.
what will happen when power factor is leading in distribution of power?
10 Answers AMET, JTO, Power Grid,
why using in cable mm square which is mm & which is square why using mm & square.
What are the industrial applications of Superhetrodyne Receivers ? What are merits & De-merits of SuperHeterodyne Receivers ?
What do you mean by S.F.U. unit? application of it.
how to make parrallal ups
How to calculate KW saving for power factor correction from 0.92 to 0.98 at 350KW load?
Hello, I am just preparing my self for a university interview and struck on the 11kv ring main unit system network. I just know that ring main unit has total three breakers, fuses and use to supply a power to any load/ building without any interrupt. But i am not be able to visualize the connections, either Ring main unit getting power from two different power sources? or there is always one feeder in complete ring circuit??? I would be highly thanks full of you help me.
why transformers not work at d.c.-
If you don’t have coal, salt and copper, then how would you earth your connection temporarily at a camp site.?
why universal motor work on ac & dc both?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)