Triping principle of ELCB&RCCB? wht is the difference
between these two?
Answer Posted / k.prakashchandra
ELCB requires earth connection. Earth wire is taken through
ELCB to the body of the appliance.If there is any leakage
current in the earth wire ,it will trip.4 pole or 2 pole
RCCB requires neutral.It works on the principle that vector
sum of the currents in phases and neutral is zero or current
balancing.If there is any leakage current to the earth it
will be sensed by only phase and not the neutral resulting
in tripping.3 pole RCCB is for a 3 phase load without neutral.
Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
Whether 3 phase induction motorwith 100 hp capacity , Amp 160 for which sensitive earth fault relay , type CTUM 15 can be used?
advantage of motor design on higher power factor . normally motors are designed for .8 power factor. what is advantage of designing at .88 power factor
There are a trformer and an induction machine. Those two have the same supply. For which device the load current will be maximum? And why?
Please give me a erda placement paper
transformer phasor diagram under load explain it?
How much costly in percentage wise is sandwich busduct costly than air insulated busduct of any rating?
describe the A.C. Generator Testing procedure
what are the applications of transistors with low dc gain, high dc gain and medium dc gain( beta)?
give single line diagram of D.G distribution form alternator to main L.T panel?
What is CVT and what is relation with wave trap?
What are the disadvantages of hydropower?
how to select diiferent power transformers of same capacity on no load loss and full load loss by economical point of view.?
what is maxemo work permit procedure
why only exciting current is shown not primary current in transformer???
why output is out of phase in case of common emitter?