Answer / chowdary
The controller name is Split Range controller.
| Is This Answer Correct ? | 8 Yes | 3 No |
Answer / divyang
There can be many reasons to provide two CV-
1. Case where flow controllability is extremly important.
Hence to get better control at lower load 2" CV will be
operated & once plant reaches cerain load higher size
control valve comes into picture.
2. Higher size CV is kept on certain value of manual
opening, and fine control is done by smaller valve. eg if
flow requried is 10000 kg/hr and controlling limits are +/-
200 kg, smaller CV will give fine control.
3. During revamp of the plant capacity instead of
increasing the existing CV, if a samller size CV is
available in spare same can be installed in parallel
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / guest
any technical reason. please clarify. With Regards-Kittu
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / ajith294
above answer is split range controller. what is a split
range control? two control valves are controled by a
controller is split range. for eg: 50% of controller out
put both of the valve will be close condition , see below
table.
% input Valve A opening %, Valve B opening&
0 0 100
25 0 50
50 0 0
75 50 0
100 100 0
but in your question on 2" valve is connected parrallel
with 6" Control valve. means for the bypassing 6" control
valve, they are using 2" valve.
for technically it is very very improtant. becasue at the
time of maintance of the control valve, there will be no
disturbance in process.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / girishkumar
It is called split range control and split a big CV into two
parts as 1:4 for fine control.ie:- in 0% both valves keep in
close. In 25% the 2" valve keeps fully open and 6" keeps
fully close. In 50% the 2" keeps fully open and 6"keeps in
25%open. In 75% the 2" keeps fully open and 6"keep 50% open
and in 100% both keeps fully open.These two valves
controlled by same controller with two AO.
| Is This Answer Correct ? | 0 Yes | 0 No |
IN JB CONSTRUCTION WHY WE ARE USING JUMPPER........CAN U PLEASE TELL ME.....
Tell me the field calibration procedure step by step with diagram of pressure gauge, pressure switch, pressure transmitter, temperature switch, level switch, flow switch, flow transmitter.
How to convertion 100 m3/hr to mmH2O or to Kg/cm2?
is there any digitel grevity meter availaible in the market by which we can measure specific gravity of a battery?
Why we using 250ohm resistance during lab calibration and why not using in field in one plz define deeply???
What is an instrumentation amplifier? How is it better than a differential amplifier when handling outputs from a wheatstone's bridge?
What is intrinsically safe system?
SIR MAY I KNOW IF RADAR TYPE LEVEL TRANSMITTER SHOWING IN THE FIELD 0 % LEVEL AND IN DCS SHOWING 100% THEN WHAT IS THE CAUSE I CLEAN THE CHAMBER & TAKEN ONLINE BUT ONLY ONCE ITS BECOME ZERO IN DCS BUT AGAIN 100% SHOWING IN DCS,THEN I REMOVE THE POWER SUPLLY AND CONNECT IT AGAIN .IS IT OK BUT STILL IN THE DCS ITS 100% AND ON THE DISPLAY ITS INITILAZIATION PLEASE HELP ME READRING THIS?
Sir, my yokugava FF TYPE LEVEL transmitter us bad, i don't have spares available, i want to replace it with a Rosemount FF transmitter, please tell me what procedure to be followed and what changes to be done in dcs part.
1 Answers BPCL Bharat Petroleum, OEG,
Flow tax range 0 to 100 mmh2o ,flow rate 40 tons /hr, I want change flow rate example 42 tons/hr so tx range ?
can we replace a pressure transmitter of range 0 to 25 Kg/cm2 by a Pressure transmitter of range 0 to 10 Kg/cm2 ?.. Will it affect 4 to 20 mA output signal which we will feed to the PLC.
Hi Friends , i need one urgent help , i am preparing for M.tech entrance examination , i need some obejective questions related to instrumentation field. where can i get those ? can anyone help me pls ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)