Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to carry out hot loop checking of closed loop pf
temperature control valve & temperature transmitter?

Answers were Sorted based on User's Feedback



How to carry out hot loop checking of closed loop pf temperature control valve & temperature t..

Answer / pratod

It can be done by following the steps below.
1. Take the control loop in manual mode.
2. Block the temperature control valve position manually to
the desired value.
3. Now check the loop as per the normal loop checking
procedure i.e. feed 4-20ma and observe the output value on
the DCS.

Is This Answer Correct ?    11 Yes 0 No

How to carry out hot loop checking of closed loop pf temperature control valve & temperature t..

Answer / senthil.doosan@yahoo.com

simple..
there is no hot loop check or cold loop check..
as u mentioned u have a temp transmitter and control valve
so,u have 2-AI and 1-AO
-connect the simulator by removing the DCS cable of the temp
transmitter,then give 4 - 20 mA and check with DCS reading
-give 0 to 100% command from the DCS for AO to operate the
control valve.then check the feedback in the DCS(AI)

conclusion,ur loop is ok...

Is This Answer Correct ?    6 Yes 2 No

Post New Answer

More Instrumentation Interview Questions

We have a Yokogawa Micro-XL DCS, which is having around 300 I/O, but whenever there is any wire gets grounded in field, the 24v supply to all loops gets dipped & all the indications at DCS goes to IOP(shows input open), at present we have fixed 500mA fuses in all the lines but which does not working. Does it required to replace with lower amps fuse, then how much or is there any other solution for this.

2 Answers  


What is the difference between modbus,fieldbus & profibus

0 Answers   NSL,


What is megering????

2 Answers  


please tel me the calibration of pneumatic controler.

0 Answers  


Can we place a Control Panel in Hazardous area Group IIC ? If 'yes' then is there any approval required? If 'yes' then there is any specific IP rating or any standard required? If 'Yes' What is MOC of control panel?

2 Answers  


List three types Level Switches with their working principles

0 Answers  


hi my name is rakesh patel i just complited my be in instrumentation & control now i am going to working as a validation engineer in a poject department so what is a scope in a future as a validation engginer ? what line is good for me can any bady give me complete solution please? your regard rakesh patel

0 Answers  


What is input and output of plc & dcs

2 Answers  


My rtd working well at the same time r/i converter is not working properly.when power is given to rtd..it is giving 30mA and getting 2.4 mA if i remove the compensate leads No matter how many ohms.why it is happening like so?what is the solution?rtd range-0-200deg c& 4-20 mA o/p.please give me solutiin anyone......

1 Answers  


how works encoder in plc

0 Answers  


In separator VFD frequently trip with OVER VOLTAGE Fault What is the reason?

4 Answers  


Furnace draft transmitter range is -50 to +50 mmwc. why the impulse line connected in hp side?

2 Answers   Arena,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)