How to carry out hot loop checking of closed loop pf
temperature control valve & temperature transmitter?
Answers were Sorted based on User's Feedback
It can be done by following the steps below.
1. Take the control loop in manual mode.
2. Block the temperature control valve position manually to
the desired value.
3. Now check the loop as per the normal loop checking
procedure i.e. feed 4-20ma and observe the output value on
the DCS.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / senthil.doosan@yahoo.com
simple..
there is no hot loop check or cold loop check..
as u mentioned u have a temp transmitter and control valve
so,u have 2-AI and 1-AO
-connect the simulator by removing the DCS cable of the temp
transmitter,then give 4 - 20 mA and check with DCS reading
-give 0 to 100% command from the DCS for AO to operate the
control valve.then check the feedback in the DCS(AI)
conclusion,ur loop is ok...
| Is This Answer Correct ? | 6 Yes | 2 No |
Ple give me "INDUSTRIAL INSTRUMENTATION AND CONTROL S.k. Singh 3th edition" Solution manual to self-Check Quiz and chapter-wise PowerPoint Slides. Home web-site not available... Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Thanks for all...
what is linerity and non-linearity?
what is maxdna ?. explain about the software details.
units for vibration in power plant
What unit is used for measuring comp. outlet flow. it is CFM, M3/hr or NM3/hr. ?
We are used CENTUM CS3000 of YOKOGAWA. please tell me how to simulate wihtout FCS and vnet.
I am a instrument technician. recently i attend interview and face one of question for DP transmitter ,the client asking about the calibration of DP transmitter ,am answer the calibration procedure, they will ask one more question. why open LP side in atmosphere? i did not answer that question. so please help me and explain the particular question. Dear firends waiting for your valuable replay
3 Answers Qatar Petroleums, Samsung,
Is it possible to convert 4 wire transmitter to convert to 2 wire with additional relay.Please send detial with drawing,i will appreciate.
Why do we need to install hook-up line differential pressure type level transmitter when the differential pressure type level transmitter with capillary are available?
Explain the difference between plc and cnc?
What is motion balance principle?
how to calibrate load cell
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)