How to carry out hot loop checking of closed loop pf
temperature control valve & temperature transmitter?
Answers were Sorted based on User's Feedback
It can be done by following the steps below.
1. Take the control loop in manual mode.
2. Block the temperature control valve position manually to
the desired value.
3. Now check the loop as per the normal loop checking
procedure i.e. feed 4-20ma and observe the output value on
the DCS.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / senthil.doosan@yahoo.com
simple..
there is no hot loop check or cold loop check..
as u mentioned u have a temp transmitter and control valve
so,u have 2-AI and 1-AO
-connect the simulator by removing the DCS cable of the temp
transmitter,then give 4 - 20 mA and check with DCS reading
-give 0 to 100% command from the DCS for AO to operate the
control valve.then check the feedback in the DCS(AI)
conclusion,ur loop is ok...
| Is This Answer Correct ? | 6 Yes | 2 No |
We have a Yokogawa Micro-XL DCS, which is having around 300 I/O, but whenever there is any wire gets grounded in field, the 24v supply to all loops gets dipped & all the indications at DCS goes to IOP(shows input open), at present we have fixed 500mA fuses in all the lines but which does not working. Does it required to replace with lower amps fuse, then how much or is there any other solution for this.
What is the difference between modbus,fieldbus & profibus
What is megering????
please tel me the calibration of pneumatic controler.
Can we place a Control Panel in Hazardous area Group IIC ? If 'yes' then is there any approval required? If 'yes' then there is any specific IP rating or any standard required? If 'Yes' What is MOC of control panel?
List three types Level Switches with their working principles
hi my name is rakesh patel i just complited my be in instrumentation & control now i am going to working as a validation engineer in a poject department so what is a scope in a future as a validation engginer ? what line is good for me can any bady give me complete solution please? your regard rakesh patel
What is input and output of plc & dcs
My rtd working well at the same time r/i converter is not working properly.when power is given to rtd..it is giving 30mA and getting 2.4 mA if i remove the compensate leads No matter how many ohms.why it is happening like so?what is the solution?rtd range-0-200deg c& 4-20 mA o/p.please give me solutiin anyone......
how works encoder in plc
In separator VFD frequently trip with OVER VOLTAGE Fault What is the reason?
Furnace draft transmitter range is -50 to +50 mmwc. why the impulse line connected in hp side?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)