why AC signals are represented by sinusoidal waveform?WHY
other waveforms not used for representation
model question paper for supervisor trainee
WHAT IS THE REASON OF CHANGE FREQUENCY IN DG SET AFTER FULL LOAD.
if we want ot select cable size with reference to load current it take than what is the formula and it is same for aluminium or copper?
( Re: WHAT SHOULD BE THE RATING OF MCCB FOR 415V,3Ph,50KVAR CAPACITOR BANK Answer # 1 The capacitor current would be kvar x 1000 / (415 x sqrt3). This would be 70a approx. The MCCB selected should have *atleast 1.4 times this current i.e. 1.4 x 70= 98. So you should choose at least 100 A mccb.) regarding to this answer,i would like to know why the current have to times 1.4 to get the right amphere for the mccb.hows the formula to get the 1.4??tq
The size and construction of bushings in a transformer depend upon?
how much maximum load a 2 core (Single phase) 16mm aluminium wire can take ?
Disadvantage of leading power factor
how to select power and control contactor .
for a 132/33kv transformer secondary is star and is connected to NER. and from secondary a cable is running to 33kv swbd. since the cable is single core do i have to run neutral cable also to 33kv swbd.???
Incoming line 11kv And transformer capacity is 2500kva. Consumption load is 1300A. Then fuse capacity is 11kv line.
why the Parameters : Base Voltage & Maximum Voltage can't be equal in value in a VFD (Variable Frequency Drive) ? How much the base voltage would be lower than the maximum voltage ? If 400 V is the 3 phase output of a VFD ... then what should be the base voltage ? thanks a lot
What is the required bending radius requied at the time of cable laying?