what is the max working temperature of an oil filled
transformer say of about 1500kva.
Answers were Sorted based on User's Feedback
Answer / sms
You can run your transformer with
1. Max winding temp up to 95 Deg.C
2. Max Oil temp up to 85 Deg.C
Is This Answer Correct ? | 14 Yes | 1 No |
Answer / k.prakashchandra
The flash point of good oil is about 125'c.You can go upto
85'c
Is This Answer Correct ? | 4 Yes | 1 No |
According to ABB,
The temperature rise limits for transformers with
temperature class of insulation A is then:
- Maximum winding temperature rise of 65ºC
- Maximum top oil temperature rise of 60ºC
If the transformer is designed for service, where the
temperature of cooling air exceeds one of the
maximum values, the allowable temperature rise for the
winding, core and oil shall be reduced
Is This Answer Correct ? | 1 Yes | 1 No |
What is Meter MF if External CT Ratio is 150/1 , PT Ratio is 132/110 Meter CT Ratio is 200/1 & Meter PT Ratio is 110/1
how the grounding[earting] is achieved on ships.
i want to put single phase load on scott connected transformer,eventhough how to balance the transformer.
If I fill the form of engineering services and I left the exam de to navoidable reasons . Will it counts my one attempt
If two hack saw blades, seperated by 1mm thick paper,are connected across 230volts, and immersed in water,then they start getting heat. This is fact,i dont know how they get heated.Blades are not directly connected together. Please if anybody knows the fact ,revert back to me
how we find transformer capacity by ohm
what is the difference between LT and HT power supply?
26 Answers Center One Mall, Central University, JSW, Siemens, Suzlon,
what is function and advantage of double delta winding in induction generator?
what is the purpose of ignitor in lighting fixer
what are advantage and disadvantage of hvdc transmission . please tell us technic of hvdc technology
How to calculate the Sizes of the cable required for one specific load? Is there any formula for that? ( EX: For 400KW load,50mtr Length, What is the LT cable Size required?)
why a motor rating in KW?