why dhyedration test required for transformer oil once in a
year
Answer / k.prakashchandra
You mean water content test? Water is likely to enter the
oil through the breather or some leakage.Water content is
not to exceed 20 ppm for voltages below 72.5 KV,10 for
above 170,15 for 72.5 t0 170
| Is This Answer Correct ? | 0 Yes | 1 No |
we have an energy meter in a capacitor bank panel, So should we consider it's readings as energy consumption on daily basis. (when capacitor bank doesn't have any energy losses)
What is the difference Marshaling box and RTCC (Relay tap changer circuit) Panel of transformer ?
How to calculate CT ratio for 11KV 1500KVA Transformer 500KVA MD and 1400KVA connected load ? Note:- As per MSEB(Maharastra state electricity Board)
what is the KVA formula of a three phase transformer
WHAT IS SPEC OF CLEANROOM MOTOR AND LIGHT FITTINGS?
What is shunt voltage and u v voltage witch one best
what is load shedding
How many double suspension hardware fittings are required on a double circuit transmission tower?
for distribution line ratio of x/r 1.<0.1 2.>10 3.>1 4.<0.01
Why do series motors have high starting torque?
before synchronizing an alternator,power factor is leading ,why?
In what cases (circumstances)we should apply P controller, PD controller, PI controller & PID controller ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)