why dhyedration test required for transformer oil once in a
year
Answer / k.prakashchandra
You mean water content test? Water is likely to enter the
oil through the breather or some leakage.Water content is
not to exceed 20 ppm for voltages below 72.5 KV,10 for
above 170,15 for 72.5 t0 170
| Is This Answer Correct ? | 0 Yes | 1 No |
in 3-phase transformer which type of transformet is used in output side?
Which of the following connection is best suited for 3-ph, 4 wire system A delta-delta B star-star C delta-star D star-delta
how to difference between the HT< cables
How do you calculate of power factor, if it is lagging or leading for unit(1).
Anybody know how schematic diagram for reverse power relay? RPR for generator protection
is there any device that works properly accept relay, it may be fuse but if i want fuse of 33kv 300 amp it is avaliable, pls give me details
Why generally the Rating of Transformers are in additions of 11 i.e. 11 kVA, 22 kVa, 33 kVA, etc........
why we are used D.c. voltage in L.T.side or controling side.we can use UPS also ,in place d.c. voltage
How many wall/floor flange will i use in bus duct system if we have in our design a 35th floor building.
how can u do the earthing of an aeroplane?
working principle of current sensing relay? how its work?
Explain role of Buckolz Relay in Transformer ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)