what voltage to be select in megger for insulation
resistance testing to L.V , H.T cables,motors and
transfomer?and ohms valve should be giga ohms only or what?
Answer / guest
You must know what is the voltage of your installation or
the cable. Eg. if its used for 230 v. Then you can use 250V
Megger or even 500V megger. For 440V application or cables
use 500V or 1000v megger.
For HT cables 3.3kv and above you can use 5kv megger.
Ohms value will come according to the reading. If reading
is in Megaohms or Gigaohms it will appear on the scale or
change tapping accordingly if any.
Is This Answer Correct ? | 26 Yes | 5 No |
what will happen if capacitor bank is used in generation side?
what is the principle of operation of tungstun bulb ??
what's producer of XLPE cable laying in undergroung
If DG runing time neutral is disconnected what will be the effect in Engine and Electricial panel.
The gauge indicates the number of amps, but what about voltage? How voltage rating (for wire or fuse) determined?
Why A.C. capacity given in Ton. Ex. - 1.5 Ton
What is mean by INRUSH CURRENT?
How can we save electrical cost i.e switchgear, wiring, conduiting etc in a room?
what is the function of breather in a transformer
29 Answers Areva, Bhel, RKM Powergen, Vijai Electricals,
wath is this mining of dg
why do we use UPF watt meter in short circuit test of the transformer and LPF watt meter in open circuit test of the transformer
Hi Everyone ! My Name is Hakim ullah khan please i need formula of Cable Rating because i want to calculate by self without check any Table Chart... Thank you.....