what is the meaning of Air condition "TON"
Answers were Sorted based on User's Feedback
Answer / parvesh1989
A ton of cooling capacity is the amount of cooling that
would be provided by melting a ton of ice. Thus, a central
air conditioning system that is rated as a 2-ton system
would provide the same cooling as melting two tons of ice
per day (24-hour period).
Ton vs BTU
A ton is equal to 12,000 BTUs. Thus, a 2-ton air conditioner
is equivalent to a 24,000 BTU air conditioner.
A BTU is the quantity of heat required to raise 1 pound of
water by 1 degree Fahrenheit.
BTUH (British Thermal Units per Hour)
Air conditioner cooling capacity is often measured in either
BTUH or tons. 1 ton = 12,000 BTUH.
| Is This Answer Correct ? | 22 Yes | 5 No |
Answer / s muthu kumar
Ton = tonage
tonage is the measuring of the Air con
it is capcity of the air condition
ex: we purchase the one tube from shop we tell like that
45Watts tube please
like that we call the air con capacity in ton(tonage)
0.5 ton ac,0.75ton Etc.....
Abouve mnetioned BTU also in a Measuring Units.
it is call British thermal Unit
| Is This Answer Correct ? | 3 Yes | 6 No |
Why the CT Secondary is rated as 5A generally?
What is sinusodial & non sinsodial current
Is KCL applicable for close circuit?
what is effect of leading power facter on the system and billing
In three pin plug 6 amp. 220V ac rating. Why earth pin diameter is higher than other two pin? What its purpose ?
how to find out cable size if load is 2800 watts, 230 volts AC supply and load distance is 1800 meters
Sir if i have 2kv ups in which 17ah 8 battries load 600watts how much back up time i get and if i put 6kv ups with the same no of battries same amp can i get more back up time please give reply exactly what is the procedure to calculate back up time for different kv,s
What is the differemce between Pulse transformer and Welding transformer.
What is the rating of HT SUBSTATION and LT SUBSTATION?
what is PDU in transformer?? which company manufacture??
Any one can explain if there is any harm from humming noise heard from air circuit breaker : we have 415 switch board having two incomers from transformers 3.3KV/415V , when bus coupler closed, and open one ACB incomer to work in one of the transformers, the current started hunting around 50 Amps, and heard humming noise from the air circuit breaker, although the load current was only 1200 amps while the ACB capacity is 2500 Amps, and the transformer 1600 KVA. The same didn't happen when taken the other transformer offline. Why this humming noise and current fluctuation? is there any implication or danger, bearing in mind that we just returned everything back to normal and stopped the maintenance of the transformer. Shall we go ahead and ignore this noise?
Impedance relay is directional relay or non directional relay?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)