How to calculate & connection of 900KVA generator
2 sets & load(1500A)?
How to choose cable size and ACB size for this load &
generator?
please explain me detail.
Regards,
Mr.Han
Answers were Sorted based on User's Feedback
Answer / subra
ACB ------- 2500A
cable size = 630sqmm X two per phase one 630 sq mm for N total seven 630sqmm cable need
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / bala_vlsi
U Can select 1600 A breaker for incoming of D.G source
and u can refere cable calouge and select the suitable
cable for 1500A THAT TIME U SHOULD CONSIDER VOTAGE DROP
CALCULATION FOR THE SELECTED CABLE .
Is This Answer Correct ? | 5 Yes | 3 No |