why generaotr rating is in kva and dc motor in kw?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
The pf is the reason ,as ac power output of alternator is
=Kvaxpf whereas the pf of dc motor is always unity and Kva
=Kw
Is This Answer Correct ? | 40 Yes | 11 No |
Answer / hemraj
generally,the rating of any machine is decide by losses of
that machine depends on what factor.losses in gen. are
depend only on generated voltage & gen. current. so rating
of gen. is in kva.
in dc motor losses are depend on voltage & current and this
losses are also depend on application of dc motor i.e power
factor of load which is connected to that dc motor. so
rating of dc motor is in kw.
Is This Answer Correct ? | 18 Yes | 9 No |
Answer / sukant
generally in case of generator n motor d rating shows d output power....in generator we get electrical energy as output having both active n reactive power.so its better 2 show in kva rating.....bt in case of motor we get mechanical power as output.....so it is represented as kw not kva............am i right???????????
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / sukesh
as we know that rating of any machine is decided by its temp
rise.temp rise due to the presence of losses in the t/f.
2 losses are there .one is iron loss and other one copper loss.
\iron loss depends on voltage.(v.i).
cu-loss depends on current.(i2.r).
so rating of t/f as well as generator both is in kva.
and for dc motor see the reply of HEMRAJ.
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / sathishkumar
generator is a source and the losses only due to current
(iron loss) and voltage (copper loss) so there is no power
factor involved so capacity is P=V*I in terms of KVA.
where as in motor there is either inductive load(laaging
P.F)or capacitive load(leading P.F)involved so capacity is
P=V*I*power factor i.e interms of KW.
Is This Answer Correct ? | 6 Yes | 5 No |
Answer / raman singh panwar
in gen. losses depend on voltage and current thus its rating is given in KVA.
but in dc motor the losses depend on voltage,current and power factor thus its rating is given in KW.
Is This Answer Correct ? | 2 Yes | 3 No |
Answer / man
the load of generator is always a mechanical load which do
not bring about any appreciable change in the power
factor.hence its rating is in KVA.where as in motor the load
is electrical load and it brings about change in power factor
so its rating is in KW.
Is This Answer Correct ? | 2 Yes | 25 No |
How can we calculate the KVA rating of a Distribution transformer from its core details?
WHAT IS RETARDATION TEST IN DC MACHINES?
there is an alternator 480 k.w, 400v,50hz, 4-wire running on load having leakage alternator body earthed current 38 A. is it within acceptable limit? if yes then give reference if no then how to bring within specified limit
After taking shutdown of 11kv feeder, if you see 5kv by phasing stick in the cable side, is it possible to close earth switch in cable.
what is a kit kat fuse?
1600 KVA ka transformer hi aghar lt side par 800A aur voltage 420 ho to HT side ki cable ki rating keya ho gi?
What happens when generator is running with leading power factor on it say -0.96. what are the effects of it on alternator and the other generators operating in parallel to it.
I am a electrical engg. diploma holder,applied for junior engineer (electrical),Kolkata RRB. Have I to attend all electrical,mechanical&civil portion in written exam.???
why do we use spark detector inside the slip ring brush compartment 0ona slip ring induction motor?
how many safety really of DG sets.
what is the effect of power factor in electrical circuit ? if we mainten power factor near about unity (0.999) our energy consumption Units increase or decrease?
11 Answers Piramal Healthcare,
what is a FACTS devices? what is mean by STATCOM????