Answer / mior
First of all, you need to know your total connected load
(TCL). Then, you apply Diversity Factor at your TCL to get
the Maximum Demand (MD).
Example;
You have 1no. 36W Florescent Lighting and 1no. socket outlet
(250W). Your TCL will be (36W + 250W) = 286W.
In actual, the TCL may only contribute certain percentage
for your MD; that's why you need to apply Diversity Factor
(DF).
Common practice, light fitting will contribute 80% and
socket outlet giving 40% for your total MD.
Hence, your total MD will be = [(36W * 80%)+(250W*40%)
]= 128.8W
Therefore, your total MD to be declared for your Utility
Provider will be 128.8W.
The link below might help your for more info.
http://guide4electricalconsultant.com/calculate%
20tcl&md.html
| Is This Answer Correct ? | 72 Yes | 13 No |
Answer / sachin
First try to know what is mean by max demand . Max demamd
is the simutaneous max requirment of power for any unit.
there is no standard practise to calculate the MD of any
unit . but one can carry out as follows.
1] CALCULATE THE TOTAL CONNECTED LOAD .
2] APPLY DIVERSITY FACTOR - IT IS THE PART OF EXPERIENCE
AND MAY VARY FROM UNIT TO UNIT .
3] TOTAL CONNECTED LOAD X DIVERSITY FACTOR = MAX DEMAND
| Is This Answer Correct ? | 27 Yes | 9 No |
Answer / yogish
There is no specific method to calculate the MD from the
CL. It really depends on the following: -
1. Type of industry: Continuous or Batch process, Heavy or
Medium or Small
2. Mechanical load or Heating load or Furnace load
3. Plant at infant stage or stabilised
4. Standby loads included
5. Largest single load and its starting method
6. Possibility of staggering load without affecting
activities.
7. Whether the major motors are optimally sized or oversized
We can get at some figure, only by experience in a similar
industry.
| Is This Answer Correct ? | 41 Yes | 25 No |
Answer / parag nikumbh
MD in KVA = (connected load in kw x Diversity factor) / P.F.
Diversity factor can be calculated as Running load/Installed load
| Is This Answer Correct ? | 20 Yes | 5 No |
Answer / j manikanta
Can you clarify my doubt.
we have a Total connected load 100 KW. We want to take an HT Connection in Andhra pradesh. So how much KVA will be sufficient for my plant. Kindly suggest me about CMD.
We will use 80-90% of Connected load. And what is diversity factor. how we need to calculate this
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / kanand078
first calculate the total load in plant. and find the
voltage and current,after u can use this formula and
calculate the MD=V*I
| Is This Answer Correct ? | 24 Yes | 62 No |
What is the difference between relays and contactor construction wise?
What does Bode plot tell you?
How PSV sizing being done
If we says that current is flow only when there is closed path & neutral work as a return path for the same. Then how circuit is closed in three phase as no neutral available ??
1 Answers Nimbus Harbor Facilities Management,
i work as a technician at a private company.. i used to take amp reading for certain appliances such as air con.. the problem is when i clamp the neutral, wire there is a current reading.. from my understanding for single phase system neutral should not have current unless if the circuit is not complete.. yet the air con still work
Hello friends, Can anyone explain the concept of zones in Bus bar protection and how can we differentiate the main zone and check zone in Bus bar protection
in control panel, how can i measuring the distance between one bus bar to another bus bar. then now only for bus bar. in mpcb and contactor also. that means one mpcb to another mpcb how much distance? how can i calculate that.
As per IS why should the control be taken only from R phase, why not from B or Y phase??!!
Why is shaft current insulation required on large motors & when should it be checked i.e. before or after assembly?
why the supply power frequency is 50hz in india? where as it is 60hz in US?
What are the condition for parallel operation of transformers?
In both 600/1000 V cable and 450/750 V cable, we can supply 415 V. However for distribution, all utilities are using only 600/100 V instead of 450/750 V. What is the reason?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)