explain why reduced voltage starters are required for large
tree phase inudction motor
Answers were Sorted based on User's Feedback
The main reason for using reduced voltage starters is to
limit the starting current drawn by the motor. This current
can be in excess of 7 times the full load current.
If the current is not limited during starting excessively
large cables must be used and larger transformers etc. to
provide the extra current.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / gopal manda
I would like to explain it by an formula of armature current:
I(Armature)=[V-E(Back EMF)]/R(Armature).
Here "V" is supply voltage and Eb is back emf which is
induced while motor running.If we not decrease starting
voltage the armature current increase very large amount.It
may damage its armature winding and its insulation.Because
at starting of motor RPM is zero so back EMF is also
Zero.That,s why We decrease starting voltage of an induction
motor.
Is This Answer Correct ? | 1 Yes | 4 No |
what is meaning of bus raiser???
what is %impedanece
What is the dimension of A4 sheet in mm?
what is purpose of manual bybass in ups
in magnetic field we send current to generate flux,why not voltage?
can we charge 3 ph power transformer delta-star wound with neutral grounded 6.6kV/415V from secondary side(415V) but with primary(6.6kV) open by dg,what are the disadvantages or losses.
please describe the Transformer setting, Motor setting, I/C setting, Tie setting
how to check the earth resistance value& what is the minimum earth resistance for good earthing sysytem.
33 Answers Brookfield, BSNL, DMRC, Epoch, KPTCL, Polycab, Power Control, SIEA, Siemens, Wipro,
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
operation principle of a generator? Gss, Diesel and HFO which is better and why?
what is the differnce b/w voltage and current
The 3 phase Delta connection RB=440V, BY=350V,.......* is Line to Line voltage RY= ? And Formula....?