Answer / debaraj das
125 KVA DG = 174A ( In 100% Load)
80% Load of 125 KVA DG = 140 A
( 80% is the Safer load you can give to your DG Set)
Is This Answer Correct ? | 59 Yes | 6 No |
Answer / guest
V= 415
KVA = 125
A = KAV/V*Root3
= 125/415*1.732
= 173.905 Per Phase
Is This Answer Correct ? | 52 Yes | 12 No |
Answer / rajesh
The best answer is 125 Amps.
Normally the best operation is carried at 80% of load.
Is This Answer Correct ? | 20 Yes | 5 No |
Answer / shridhar awasthi
125 kva dg will take 173.90 amps on 100% loading and 191.29
amps at 10% over loading according to I=KVA/sqrt3*voltage
Is This Answer Correct ? | 13 Yes | 4 No |
Answer / nadhan
Why should not we add the capacitor bank for dg set alternator to minimize the dgset load current.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / sk aminul hossain
Amp=kva*p.f/volt*root3 So
125*1000*0.85/415*1.732 (k=1000,v=415,p.f=0.85) reactive power
So, amper=147.81A or 148A
Is This Answer Correct ? | 1 Yes | 1 No |
How to calculate the current rating of power cables ?
What is the function of Buchholz relay in transformer ?
WHAT IS THE FUNCTION OF SHORT CIRCUIT MAINTENANCE CT
in an ac series circuit there are 30 bulbs are connected in a serial set.what will happen if one bulb is fused and we removed the bulb and reconnect with the remaining bulbs? (29 bulbs). will the brightness of other bulbs increase or not?
what is the use of expulsition protective gap in 11Kv line.
What are the disadvantages of hydropower?
What is the difference between grounding & earthing?
what will happen if any motor runs long time with star connection in400vA.C. system
Any website for objective type questions of electrical engineering ?
any body can give me idea or sketch of fuel(Diesel) level controller for genset.
why transfromer rating gives in MVA Or KVA? Why not in MW or KW?
In Energy meter How many rotation Equal to one unit.