How to calculate the size of the cable? for exp i want to
use the load of 10HP
Answer Posted / santosh
Sqmm of cable depends upon the cable material.In thumb rule Cu cable can carry 10-12 times of its rated sqmm.For ex 10 sqmm cu cable carry 100-120 amps.Al cable carry 4 times current of its rated sqmm
For ur problem: 13A is rated current. 50-60 amp staring current,7-8 running cu.So u may need 4 sqmm Al cable or 2.5 sqmm cu cable.
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
sir, what is the importance of Fault MVA. how to calculate fault mva of 33kv substation connected by 6.5 km line(single circuit with equal spacing) with 110/11kv transformer in 110kv susbstation.the fault mva on 11 kv bus in 110kv susbstation is 208mva.
Phase control and integral control are used for?
from which formula we select a capacitor rating?
what is conductor copnstant of ab cable
explain why core loss of a transformer is almost constant under different load conditions when connected across a constant voltage and constant frequency.
list the type of vfd? wich is sutable for heating kiln?
High voltage test procedure of in swgr board. why should measure millivolt drop on testing time?
Write the force balance equation of ideal spring element.
Which device is used for the source of emission of electrons in a crt?
HAI SENT HPCL APTITUDE QUESTION PAPER, MY EMAIL ID IS angus_eee04@rediffmail.com,angus_eee04@yahoo.com
Best way to measure the Soil resistance of rocky soil, three probe method and four probe method
How PADO software increase the efficiency of power plant?
what is the size of ht cable of 33kv ht line and transformers ratings are 1 Mva and 5mva.please send formula also.
i need the details about bhel exam.how to apply for that.please send to my email-id.thenmozhi2k7@gmail.com
Merits & Demarits of Oil circuit & Air circuit breakers ?