what will be fault level of 11 KV , 2000 A ELECTRICAL
SYSTEM?
Answers were Sorted based on User's Feedback
fault level depends on your system's percetage impedance.In
general practice we are using 28KA for 3 secs. or 40KA for
3 secs.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / genau
Mr. Ranjan is correct!!
Fault level of the system will depend on the system impedance.
for calculation of fault level, calculate the fault impedance and hence you can calculate fault current from system voltage and fault impedance. product of two gives fault level in VA (Generally specified in MVA)
Is This Answer Correct ? | 0 Yes | 0 No |