Answer / iamdon
CT is used mainly for Instrumentation(Measurement and
protection system) purposes that is why it is also termed as
instrument transformer.The measuring and protecting devices
are not rated to sustain high currents.What a CT does is,
it lowers the current in secondary side so that measurement
as well protection can be done at a reduced level of
current.
The digit in CT ratio of secondary side is IS standard for
rated secondary current so that uniformity among manufactures
be established.
The various values of secondary currents are
1)in the range of 0-5 amp e.g, 1A,5A
2)in the order of mA(particularly 40mA)in case of digital
devices for measurements and protection.
Author:arbelectbit@yahoo.com
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / k.prakashchandra
With introduction of electronic protection and
metering ,nowadays 1A secondary CTs are employed.
| Is This Answer Correct ? | 1 Yes | 1 No |
which type of breaker sould be used for different level of voltage ? (i.e at 11 Kv, 33 Kv, 66 Kv....
what is disadvantages of high power factor
a)In a 3-phase 4-wire circuit, a circuit breaker is selected to protect the circuit whose highest fault level is 6.6 MVA. Determine the required minimum breaking capacity in kA. (Note: Covert 3-phase power in terms of kA to find answer.) b)Using the below, determine the required minimum making capacity in kA as a “peak value”. Rate breaking capacity (Icn) ka: Icn<= 1.5 Factor = 1.41 1.5
In industries Power factor is maintained by installing a suitable KVAR bank, How is the PF maintained for domestic use, where is the capacitor bank connected
what are the standard values for resistances(Megger testing) between L&N, L&E and N&E (L=Live,N=Neutral, E=Earth)?
What are all the conditions to protect generator & turbine in thermal power plant?
Which power will flow first if we switch on a motor? Active or Reactive? How?
A powerplant has 8 gensets operating in grid parallel mode. In one genset sometimes there is pf variation and kvar variation. The plant operates in pf mode. When this variation is observed the load is stable, voltage is also stable, freq and genset speed is also stable. How will you check the functioning of pf card. What shall be the ideal output vdc of the pfc, from there it is input to AVR?
Name different types of fault and which instrument is used to measures earth,short,open cicuit fault?
6 Answers NTPC, Vijai Electricals,
Form S and "c" license application both are same? @ tneb portal
What is PF? Formula for calculating PF in HT side?
what are the deffects for failure of PLC?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)