what sud u do if u dont get feedback from control valve?
Answer / carl_ellis
There's two kinds of feedback from a control valve:
a) the change of the process variable because the valve
position changes
b) position feedback directly from the positioner to the
controller/control system.
We'll assume that the question is directed at the loss of
position feedback signal from the loop's positioner.
1) Position feedback cards are options on smart
transmitters and need to be initialized after installation.
Has it been initialized?
2) DC power is typically loop power for position feedback.
Is the loop power supply still functioning?
3) Has the position feedback card or its wiring been
disabled or removed?
4) If the position feedback loop is intrinsically safe, is
the loop's I/S barrier open circuited?
5) Has the loop wiring been changed in some manner so as to
affect the position feedback signal integrity?
Carl Ellis
Measure First
Is This Answer Correct ? | 8 Yes | 0 No |
What is Loop Test & What is Loop Checking? Please i need answer for these questions.
yokogawa Temperature transmitter showing Error 15 which is Reverse Cal Fail (confirmation calculation result is bad) in manual they mentioned reasion That the output goes to the value set by hardware failure mode jumper. How can solve this problem ? anybody can say solution
What is the difference between ROM & RAM .
for oil & gas industries which zone is normally preferred? why? give its example?
modbus and profibus communication difference?
how many pulses are required by a ac induction servo motor of 4 poles with 50 Hz frequency to rotate by 1 degree?
What is difference b/w absolute & gauge pressure? EXPLAIN
what does ip65 signify??what is its NEMA equivalent???
need instrumentation job completed 1 year trainee ship in mnc pesticide company. now in search of job
What is eddy current? Describe the operating principle of proximity probe.
Why we use negetive (-)voltage in vibration system
Hi, I'd like to know the purpose of MOS (maintenance override switch). At site, these switches are installed in a stanchion with the transmitter (connected to ESD). thank you.
3 Answers Adani, Adani Wilmar,