How can we calculate the capacity of the capacitor bank
attached with the Main panel, when we know the capacity of
the panel installed in KVA Rating?
Answers were Sorted based on User's Feedback
Answer / sanjeev nair
The formula for calculating the Capacitive kVAr required to
compensate inductive kVAr is kW*sqrt(tan_angle1-tan_angle2).
In your case, you have to check the present power factor
and then the kW.
Suppose, If you have load of 50kW and the power factor is
0.8 and you have a plan to improve the PF to 0.95 then as
per the above formula the Capactive kVAr required to
compensate the inductive kVAr would be 21.
Besides, one should understand and work on the application.
ie, you can go for a 20 kVAr capacitor bank as per the
above if you have 50kW motor working on a pf of 0.8. If
both load and inductive kVAr is varying, then you have to
go for automatic pf control system with suitable banks to
compensate the inductive kVAr.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / chiknabacha
http://www.newindiaelectricals.com/newindia/exports/capacitor/calculation.htm
Please find the calculation for KVAR from the required table
| Is This Answer Correct ? | 0 Yes | 0 No |
While HT line put on to activate ACB in low tention panel VCB tripping instantly.why it happens
what is the interrelation between voltage current torgue speed and magnetic flux in case of different types of electric motors
What is the important precuations need tocarried out while working with Electrolite in Battery PM?
Does the dg syncronization sucessful in practical.
what are the shades for mimic diagram i.e for 3.3kv,6.6kv,11kv,22kv and 33kv? which is the IS for mimic diagram?
in power station what is the electrical circuit length of spacing between power transformer and lightning arrestors,for the voltage system of 230kv,110kv,33kv,22kv,11kv?
a 100mva,400/200v transformer has leakage impdce of 10% draws a steady state line currentof---------------
why maintain the Dg PF is 0.8? Explain?
how much amps will get from a 360/11kv line
sir What is the different bet'n "Active & passive" sensors
If a earth leakage circuit breaker trips is it possible to tell which house circuit breaker (I have four) is the faulty circuit?
why we use 110vac in overhead crains? why not 220v, 24v
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)