Answer / sanjeev nair
The formula for calculating the Capacitive kVAr required to
compensate inductive kVAr is kW*sqrt(tan_angle1-tan_angle2).
In your case, you have to check the present power factor
and then the kW.
Suppose, If you have load of 50kW and the power factor is
0.8 and you have a plan to improve the PF to 0.95 then as
per the above formula the Capactive kVAr required to
compensate the inductive kVAr would be 21.
Besides, one should understand and work on the application.
ie, you can go for a 20 kVAr capacitor bank as per the
above if you have 50kW motor working on a pf of 0.8. If
both load and inductive kVAr is varying, then you have to
go for automatic pf control system with suitable banks to
compensate the inductive kVAr.
Is This Answer Correct ? | 4 Yes | 3 No |
Answer / chiknabacha
http://www.newindiaelectricals.com/newindia/exports/capacitor/calculation.htm
Please find the calculation for KVAR from the required table
Is This Answer Correct ? | 0 Yes | 0 No |
while doing high voltage test on 11kv/433 distribution transformer why we only give 28 kv on hv side and 3kv on lv side for power transformers what is the value what factors it depends
Weather power factor correction needed for synchronous motors?
how could we calculate the no of outgoings from a 800 watt distribution board
How Diesel Generator start ?
0 Answers ITC Infotech, Voltech,
CAN ANYBODY EXPLAIN WHAT ACTUALLY MEAN BY THE PHASE DEFFRENCE? R,L,C CIRCUITS?
cany anyone suggest electrical wesites for providing study materials?
why current is leading in capacitor?
what is the thumb rule to know current carrying capacity of copper conductors of different size.
physical identification of HT & LT panel
IF avr is voltage regulator of genset means why we are giving genset CT sense to AVR ?
what is meant by reactive power ,active power & real power ? thank you
Meter p.t. ratio= 3×230/400 , c.t.ratio = 3×1 (2) A what is m.f.