present we are having 0.8pf but I want increase it up to
0.99 so what is the formula for it and how can i calculate?
Answers were Sorted based on User's Feedback
Answer / kuppuswamy
PF = KW/KVA That is power factor = True power divided by
Apparent power.
If you want to increase the PF in generator, you have to
adjust the speed and voltage to bring to the required PF.
If you want to increase PF in industrial load, you have to
go for adding the capacitor banks in the line side.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / satheeshramesh
If u wish to increase the P.F from 0.8 to 0.99 u have to
add capacitor banks.
Capacitor rating required (kVAR) =kW(tanØ1-tanØ2)
Cos Ø1 = 0.8, Ø1 = cos-1 (0.8), tan Ø1 = .
Cos Ø2 = 0.99, Ø2 = cos-1 (0.99),tan Ø2 = .
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / at
if you want to increase the power factor from 0.8 to 0.99
then in that case for
1. Generators:- you will have to increase the excitation
when generator is connected in an interconnected system
i.e. Many generators operating in parallel / or connected
to grid. increasing the excitation gives a leading power
factor and under excited generated draws lagging power
factor power.
2. When it is the case of Industries or other utilities
consuming electrical energy. one should know that all loads
consuming power are 99.99% inductive loads.Thus by adding a
capacitor bank of suitable rating shall be required to
compensate the lagging power factor.
| Is This Answer Correct ? | 1 Yes | 0 No |
Why oil preferred over the air as a cooling medium for high rated transformer?
NOW A DAYS THE POWER SUPPLY IS VERY LOW.SO THE FLURESCENT TUBE LIGHTS ARE VERY DIM.IS THERE IS ANY WAY TO INCREASE ITS BRIGHTNESS?FOR EXAMPLE ANY CONVERTER,CONDENSER?
In my power station 220 volts dc battery set. they coneected 84th cell taped
what law motor works?
what is inverter and converter
7 Answers Shrishti Power Technologies,
transformer is working or not with supply of DC?
why transformer rating in kva?
suri transmission
What is a slack bus?
DEAR ALL I have motors ( 10 units )each one is 90kw 380V 50 HZ 1000rpm but new local pwer is 220v 60 hz requierd rpm should be 1000 pleas what the beast solution is used frequncy converter or rewinding all motos or chang all motors thanks
why all selected supply voltage are multiple of 11
What is multiplying factor of meter if the meter ctr and ptr is open type?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)