1.What do you mean by inductive and capacitive parts of an
electric circuit. 2.What do you mean by decrease of
inductane and capacitance of a network? Please dont give me
the text book answer.3. What is class X ct and its
applications?
Answers were Sorted based on User's Feedback
Answer / satendra
1.The element of circuit due to which the current lags is
Inductive part and part which lead the current is Capacitive
one.
2.It's simply shows the performance of the circuit
3.sry
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / sayan
Class PS/ X CT: In balance systems of protection, CT s with
a high degree of similarity in their characteristics are
required. These requirements are met by Class PS (X) CT s.
Their performance is defined in terms of a knee-point
voltage (KPV), the magnetizing current (Imag) at the knee
point voltage or 1/2 or 1/4 the knee-point voltage, and the
resistance of the CT secondary winding corrected to 75C.
Accuracy is defined in terms of the turns ratio.
Is This Answer Correct ? | 0 Yes | 0 No |
How seriving & testing of the HT & LT breakers are done. What are the standard Ir values on which we can come to know the test is passed or failed?
what is onan, onaf, ofan, ofaf in transformer?
What is the selection & Designing procedure for DG/Transformer
4 Answers Crompton Greaves, Sterling, TATA,
If single phase voltage level is 230V than why three phase voltage level is not 660V ?, but it is only 440V.
16 Answers BSNL, DOS, EFS, HMT, L&T, TCS, ThyssenKrupp,
Frequency of rotor emf in induction motor is around A same as stator frequency B 50% C 5 % or below D 30%
Why Delta Star Transformers are used for Lighting Loads.
how to improve IR value in HT motors?
what is the role of impedance in transformer?based on secondary f.l.current(139 amps) and impedance(4.07) of 415/415v of 100 kva transformer. what is the primary current?
why open-delta core of 11kv Potential Transformer is 11000v/1.732/110/3?
What is the formula for calculating no-load current?
Enlists the applications of sampled data systems?
Is it possible to run HT motor through LT VFD (LT VFD supply given to Transformer LT side and transformer HT side connected to motor)