Is it alright to connect more than one RCCB of same rating
in series for a three phase equipment?
Answers were Sorted based on User's Feedback
Answer / s c budhiraja
No, it is of no use to connect more than one rccb of the
same rating in series for a three phase equipment.It is
only waste of money.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / electrobot of the philippines
why you need to connect series of RCCB's by the way?? its a
stupid act.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.suresh
it leads more maintenance and more work during
fault.also,series connection will not give additional
protection and some time we may face neusence tripping.
Is This Answer Correct ? | 0 Yes | 0 No |
How to justify this statement ??? "Capacitors in series provide less capacitance but higher voltage breakdown rating for the combination"
what are the advantages disadvantages of connecting high voltage block( 1:1 transformers) transformers between the turbo generators and busbars.
What is the main difference b/t Earth leakage relay & Earth fault relay.I want protect my LT panel(Distribution Panels)which relay have to propose.......
What is George phenomena to start the synchronus machine?
Why frequency changes due to load variation in power system ? i.e why when load increases frequency decreases?
what is IP55,IP65
freuency meter
sir please tel me how calucalte kwh if home taken load 30ams how maney kwh taken per day.and 3phase motor 5hp per hars how maney load teken and how mach kwh and forward me to electrical table for calicalte kwh and kvr and kvah
Please help me regarding my one concern. - During earth pit testing we noticed that the Clean earth pit and dirty earth pit showing continuity (Resistance value - 5ohm) . I want to know that if both earth pit have separate location and there is not internal looping between PIT then why such continuity is showing on it . Because of this issue the field side all earthing point showing short. In PLC panel we are providing two types of earthing cable which is coming from separate earth pit (Clean and Dirty earth pit) because of earth PIT showing short our PLC is not complying spec . please help regarding this issues.
how much rating of fuse and MCB should be used for a load consisting of 6KW and 18KW inductive load?
why the transformer ratings in kva or mva?
why we not using 230kv directly why we are stepping down and then stepping up