what is full form of dyn11( in transformer)
Answer Posted / anil
the first letter must be capital one, which represents HV
winding while second letter should be lower case, which
represent LV winding of transformer.
1. 'D' - HV winding is delta connected & 'Y'- HV winding
is star connected
2. 'd' - LV winding is delta connected & 'y'- LV winding
is star connected
And rest of number indicating phase displacement angle
i.e 1 = 30°, 2 = 60°, 3 = 90°, 6 = 180° and 12 = 0° or
360°.
so
Dyn11 indicates,
Delta connected HV winding, star connected LV winding with
neutral brought out, LV is leading HV with 30°
Is This Answer Correct ? | 13 Yes | 1 No |
Post New Answer View All Answers
What are the different types of controllers?
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
what is calculation mathod/formaulla for deciding Size of busbar (Copper/ aluminum)for L.T. panel on Various Fault level like 50kA,25kA,10kA
CAN WE CALCULATE THE NEGATIVE SEQUENCE AND ZERO SEQUENCE REACTANCE OF A GENERATOR USING ONLY ITS RATED VOLTAGE, KW, PF AND SYNCHRONOUS REACTANCE??? IF YES, THEN HOW??
hi frnds...pls send me aptransco previous papers .....pls..pls,,,(madhar.rocking@gmail.com)and suggest me some websites
how is capacitor bank look like
I have doubt that the supply HZ (very low or high than rated ) may affect the power factor. is it true. ?
what are the difference between AC lamp and DC lamp
sir i ve applied for hindustan petroleum and power grid india ltd..and the exams on feb 22.can you pls send model papers and tell how to prepare for those.i need to get into any of these for sure.....
Draw a SLD of HT distribution EB grid up to users Transformer?
How can we calculate the transformer rating if the load calculated is 1000KW (11Kv Supply)?
I am experienced with house and industrial wiring but I don't have any licence how can I apply an licence and which type of licence i can get i didn't complete deee just only experience
What happens to a motor if it is connected in Delta connection
How to calculate wire length,size & current? ( related to control panel)
IF 8255 CONTROL WORD IS 94H,Tell the chip port work mode ?