why do we provide metallic enclosure to bus duct and then ground it?
Answer / aarya
The insulation between the lengths of duct and the insulation between each length and ground serve two purposes. One of these purposes is to prevent the eddy currents induced in a particular duct from circulating between that particular duct and the adjacent ducts and also between that particular duct and the grounded supporting structure for the ducts, thus preventing the undesirable heating which tends to result from such circulating eddy currents. The other of these purposes is to direct faults that occur to the duct to ground via a path extending through a ground return bus.
Is This Answer Correct ? | 6 Yes | 0 No |
control & auxilary circuits used for circuir breakers
why can tv operate at low voltage??
What is the difference between type1 and type2 relay protection co-ordination for motor feeders
If u have 60KVA UPS, than tell me how systems ( computers ) u may connect?
how to calculate current carrying capacity in power cable?
power transmission pole used one support , that only for support or earthing
What is the difference bet ween EDO Type & MDO type ACBs, and what is the advantage EDO Type over than MDO type ACBs.
advantages & disadvantages of Lagging and leading power factor .
can we coorect P.F. OF 320 KVA ALTERNATOR AT LOCAL SITE WITH RATED .8 PF LAGGING.
If we know the load for generator in KW then how it will be change to amps and also if we know the load in amps how it will change in KW and what Generator is good for that...suppose load is 500 amps 3phase......??
why is neccessary Tap changing of power transformer with in a certain time
How to calculate cable size by using load.?? Any formula...