what is difference between delta-delta,delta-star
transformers
???
Answers were Sorted based on User's Feedback
Answer / eduardo
In a delta connection you don´t have any access to the "mid
point" or if you prefer to the "neutral".
In a star connection you will have a four(th) terminal, that
you can connect to earth or use it as neutral conductor.
For example if you have a three phase power line at 15 kV,
and want 400 V and 230 V you can connect the primary in
delta (you don´t need the extra connection) and the
secondary at star. (delta- star)
Now you will have 400 V between any 2 phases and 230 V
between one phase and the star point of the transformer.
If you connect the secondary in delta you will not have 230
V, because you don´t have the 4th terminal. (delta-delta)
Please note that in star one winding of the transformer will
have 5,8 kV (10000V / sqrt(3)). In delta connection you will
have in one winding 10 kV. So verify the tension and the
connetction type of the transformer. (both primary and
secondary).
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / shahbaz shaikh
in delta-delta transformer primary side and secondary side of transformer are connected in delta fashion i,e R-Y-B are connected in triangle fashion these are generally prefer for the transmission system and here no neutral point is present and for the distribution system we use the delta star because our home appliances are work at 230v but in 3 phase we have 440v so to get the 230v we use delta primary and star secondary so by using one of phase and neutral point of star we can get the 230v.
| Is This Answer Correct ? | 0 Yes | 0 No |
Thermal withstand capability under full short circuit conditions, in terms of number of times of occurrence of short circuit and corresponding anticipated percentage reduction in transformer life.
what is frequency transformer?
what is the operation of regulator in fan?
What are various power system instabilities and what are their effects on power system operation?
what is percentage impedance of transformer? explain its significance
physical identification of HT & LT panel
HOW DO WE COLLECT THE SOLAR ENERGY AND DESCRIBE THE METHODS TO CONVERT THE SOLAR ENERGY INTO ELECTRICAL ENERGY?
What are the conditions to be satisfied for parallel operation of dc generators?
What is differnce b/w tie breaker and bus coupler?
Can you use step up generator transformer of voltage ratio 16.5kv/420kv in place of step up generator transformer 15.75kv / 420 kv
why we use RYB phase sequence? and somewhere we use UVW ? why?
6 Answers CSPDCL-Chhattisgarh State Power Distribution Company Limited, MUET, TCS,
What is application of MCB & How it works
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)