Explain Buccholz relay in detail.
Answers were Sorted based on User's Feedback
Bucholz relay is connected in between the manin tank and
conservator tank and in an angle, when the faults like
loose connection or heat desipation from winding occurs the
gas buble is produced in the oil. As the conservator tank
is installed above the tank level the gas buble trys to
travel to the conservator tank, in between the bucolz relay
is there the gas buble gets trapped in the bucolz relay and
it presses the flot in bucloz relay to down words and it
will activate for once in lot of faults like gas develops
if sudden major fault like short CKT it will activate
imediyetly
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / yanamadalaashok
Buchholz relay is a gas- actuated relay installed in oil-
immersed transformers for protection against all kind of
faults. It is used to gives an alarm in case of slow
developing faults or incipient faults in the transformer
and to disconnect the transformer from the supply in the
event of severe internal faults. It is installed in the
pipe between the conservator and main tank.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / roysayan01
plz explain the working dude...how does the mercury buckets
actually work???
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / basavaraj patil
Buchholz relay is a gas- actuated relay installed in an oil-
immersed transformers for protection against
faults. It is used to gives an alarm in case of slow
developing faults or incipient faults in the transformer
and to disconnect the transformer from the supply in the
event of severe internal faults. It is installed in the
pipe between the conservator and main tank.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / anbarasandurairaj
Bukolz relay is a gas operated relay used to protect oil immeresed transformer from fault it is located between conservetor and transformer tank if there is any minor fault inside transformer relay trigger the alarm, major fault relay trigger the gripping cicuit and protect the transformer from fault.
Is This Answer Correct ? | 0 Yes | 0 No |
There is 15 KVA UPS using for single phase load.And 30 batteries of 12 V, 100 Ah are connected in series. Load is taking 15 A current.What will be the back up power for this UPS on same load?
1 Answers BS, Dynamic Software,
WHY WE GENERATE 3 PHASE POWER ONLY AND NOT 4 OR 5 OR 6 PHASE??? PLS REPLY.
AC SUPPLY HAVING 230 V FREQUENCY REDUCED ZERO IF MEN TACUCHES THE SUPPLY WEATHER HE GETS SHOCK OR NOT?
why transformer ratings in kva?
99 Answers Bhel, College School Exams Tests, DOW, Emco, Esab, GE, KCP, PGCVL, Sodexo, TCS, vtps, Wipro,
What will be the current drawn by HT motor, if low voltage is applied.. any formula to calculate the LT amps of HT motor.?
which type of motor is used in lift ?
what causes contact chatter when there is no demand on the air conditioning unit?
How will calculate losses in an multi core Aluminium LT cable of different sizes & upto what length we can use a LT Cable ?
is there any concept of armature reaction in Induction motor?
is electrons really flow or they just vibrate at their position?
why neutral and body earthing of transformers kept separated? what is distance between two is required as per is?
why do star-delta connection ? why do not connect any circuit direct connection ?