Bucholz relay is connected in between the manin tank and
conservator tank and in an angle, when the faults like
loose connection or heat desipation from winding occurs the
gas buble is produced in the oil. As the conservator tank
is installed above the tank level the gas buble trys to
travel to the conservator tank, in between the bucolz relay
is there the gas buble gets trapped in the bucolz relay and
it presses the flot in bucloz relay to down words and it
will activate for once in lot of faults like gas develops
if sudden major fault like short CKT it will activate
imediyetly
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / yanamadalaashok
Buchholz relay is a gas- actuated relay installed in oil-
immersed transformers for protection against all kind of
faults. It is used to gives an alarm in case of slow
developing faults or incipient faults in the transformer
and to disconnect the transformer from the supply in the
event of severe internal faults. It is installed in the
pipe between the conservator and main tank.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / roysayan01
plz explain the working dude...how does the mercury buckets
actually work???
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / basavaraj patil
Buchholz relay is a gas- actuated relay installed in an oil-
immersed transformers for protection against
faults. It is used to gives an alarm in case of slow
developing faults or incipient faults in the transformer
and to disconnect the transformer from the supply in the
event of severe internal faults. It is installed in the
pipe between the conservator and main tank.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / anbarasandurairaj
Bukolz relay is a gas operated relay used to protect oil immeresed transformer from fault it is located between conservetor and transformer tank if there is any minor fault inside transformer relay trigger the alarm, major fault relay trigger the gripping cicuit and protect the transformer from fault.
| Is This Answer Correct ? | 0 Yes | 0 No |
purpose of flux relay for turbo generator in power plant
What difference between ref protection and differential protection ?
0 Answers EPC, INEL Power System Engineers,
Why we are testing cables with dc?
what is rms value?
What do you mean by pf of a generator? Power factor purely depends on the load (wether inductive, reactive or unity) then what does the pf mentioned on the generator nameplate means?
why the rating of a transformer in kva not in kw.
in dc machine airgap is there b\w stator and armature but by conduction emf is generated how & what is conduction
How many loops can be provided in a circuit as per IS rules.?
What happen to generator if i have unbalanced load?
0 Answers Reliance Energy, Sail, TCS,
What is the role of the 50 STUB protection at a GIS 400KV substation with SIEMENS protection relays?
A 6.6 KV/ 440V Xformer. what are the imporatant parts & equipment required for it's protection panel.
Motor running trough VFD, if voltage reduced speed will be?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)