Explain Buccholz relay in detail.
Answers were Sorted based on User's Feedback
Bucholz relay is connected in between the manin tank and
conservator tank and in an angle, when the faults like
loose connection or heat desipation from winding occurs the
gas buble is produced in the oil. As the conservator tank
is installed above the tank level the gas buble trys to
travel to the conservator tank, in between the bucolz relay
is there the gas buble gets trapped in the bucolz relay and
it presses the flot in bucloz relay to down words and it
will activate for once in lot of faults like gas develops
if sudden major fault like short CKT it will activate
imediyetly
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / yanamadalaashok
Buchholz relay is a gas- actuated relay installed in oil-
immersed transformers for protection against all kind of
faults. It is used to gives an alarm in case of slow
developing faults or incipient faults in the transformer
and to disconnect the transformer from the supply in the
event of severe internal faults. It is installed in the
pipe between the conservator and main tank.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / roysayan01
plz explain the working dude...how does the mercury buckets
actually work???
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / basavaraj patil
Buchholz relay is a gas- actuated relay installed in an oil-
immersed transformers for protection against
faults. It is used to gives an alarm in case of slow
developing faults or incipient faults in the transformer
and to disconnect the transformer from the supply in the
event of severe internal faults. It is installed in the
pipe between the conservator and main tank.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / anbarasandurairaj
Bukolz relay is a gas operated relay used to protect oil immeresed transformer from fault it is located between conservetor and transformer tank if there is any minor fault inside transformer relay trigger the alarm, major fault relay trigger the gripping cicuit and protect the transformer from fault.
Is This Answer Correct ? | 0 Yes | 0 No |
How to dimensioning SDCCH, LAPD and CS7 signaling on GSM?
Two CTs 1600/1 and 35/1 are in series. while checking the ratio test of a CT(1600/1),same 1600A will also pass through the CT having ratio 35/1. Will it be harmfull to the ct(35/1),if yes , what will happen.CT secondary is shorted
Dear All, In a 400V power system, ratio of three current transformers installed incoming switchgear is 4000/1. Maximum three phases short circuit current of this system is 48kA. One CT is installed on neutral of upstream transformer (6/0.42kV, solidly earthed) for 51G protection. Would you please inform me about the correct CT ratio of this current transformer (on neutral)?? Thanks a million
Why PT burnts?
what the purpose of protection signaling equipment in substation?
if the diameter of a conductor is 'R' then what is the distance between two bundle conductor in a phase?
1.what type of wave is produced from i.online ups ii.offline ups iii.inverter.why don't we use inverter instant of offline ups for computer,what's the reason?
What is the working of Field winding in dc motor, in which part is it work or why ?
During underground cabling in landscape area what did we cover the cable with to prevent the electric shock & protect the cable?
what is real and reactive power?
i ha done my 10th with 71% ,ITI with 81% 11th with 75% 12th 43% apprentiship with 71% in SAT i secure 1390 ,TOEFL 27 i was refused four times and in all me interview visa officar told that i am not Qualify for study in USA but i completed my 12th yes i got low persentage in my 12th but i seen to much student they already got visa with them 3 or 4 backlocs so why they are refused me ?
opkinson's test