Explain Buccholz relay in detail.
Answers were Sorted based on User's Feedback
Bucholz relay is connected in between the manin tank and
conservator tank and in an angle, when the faults like
loose connection or heat desipation from winding occurs the
gas buble is produced in the oil. As the conservator tank
is installed above the tank level the gas buble trys to
travel to the conservator tank, in between the bucolz relay
is there the gas buble gets trapped in the bucolz relay and
it presses the flot in bucloz relay to down words and it
will activate for once in lot of faults like gas develops
if sudden major fault like short CKT it will activate
imediyetly
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / yanamadalaashok
Buchholz relay is a gas- actuated relay installed in oil-
immersed transformers for protection against all kind of
faults. It is used to gives an alarm in case of slow
developing faults or incipient faults in the transformer
and to disconnect the transformer from the supply in the
event of severe internal faults. It is installed in the
pipe between the conservator and main tank.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / roysayan01
plz explain the working dude...how does the mercury buckets
actually work???
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / basavaraj patil
Buchholz relay is a gas- actuated relay installed in an oil-
immersed transformers for protection against
faults. It is used to gives an alarm in case of slow
developing faults or incipient faults in the transformer
and to disconnect the transformer from the supply in the
event of severe internal faults. It is installed in the
pipe between the conservator and main tank.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / anbarasandurairaj
Bukolz relay is a gas operated relay used to protect oil immeresed transformer from fault it is located between conservetor and transformer tank if there is any minor fault inside transformer relay trigger the alarm, major fault relay trigger the gripping cicuit and protect the transformer from fault.
| Is This Answer Correct ? | 0 Yes | 0 No |
when meggering a 3ph,480v oil reservoir heater on a regen gas compressor, why do I get a reading to ground when meggering phase to ground? shouldn't it read opened or is there something that makes it read closed? on the same heater, when ohming, it reads open. thanx
Dear All, In a 400V power system, ratio of three current transformers installed incoming switchgear is 4000/1. Maximum three phases short circuit current of this system is 48kA. One CT is installed on neutral of upstream transformer (6/0.42kV, solidly earthed) for 51G protection. Would you please inform me about the correct CT ratio of this current transformer (on neutral)?? Thanks a million
Now I inject 1kv DC supply r&y=??? R&Y=?? Y&B=?? B&R=???? RYB&N=??? RYBN&E=????? Minimum value====???????
Why we use mho Relay in long transmission line?
what is the length of air terminal in lightening arrester system.
WHY THE COLOR OF OUTDOOR TRANSFORMER IS BLUE ONLY???
what are factors to be consider to design a HT & LT motor?
how can u say about the line by looking at the tower ? {voltage rating of the line}
what is difference between RCB,RCCB &RCBO?
how to design coil turns ?
Why do we use center tap transformer that used with portable tools
If the generator will not synchronize, what will you do?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)