How the oil level of the Buchholz Relay come down.
Answers were Sorted based on User's Feedback
Answer / sajid hussain
When load increase on the secondary side of the
transformer,heat produced which decompose the oil i.e
hydrogen and carbon. This lightly Hydrogen gas entered in the
Relay Dom and produced pressure on oil at the upper side. The
oil level of relay housing decrease.If the heat produced is
too higher due to current flow or arc the decomposition of
oil is also high which cause the more oil level down in the
relay housing.
Note Any correction please send email
msajid1980yahoo.com
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / guest
The Buchholz relay functions by making use of the liberated
gas inside the transformer due to an internal fault, to
actuate an alarm or trip the circuit breaker depending on
the seriousness of the fault. The virtue of buchholz relay
is that it detects an incipient fault i.e in the very early
stage itself before serious damage is done, whereas others
relays operate after the fault has occurred. Therefore
repair measures are simpler. Example of incipient faults are
short circuited core laminations, broken down core bolt
insulation, failure of inter turn insulation and consequent
local over heating , bad switch contacts and faulty joints etc..
The relay comprises a cast iron housing inserted in the pipe
connecting the transformer tank with the conservator tank.
It consists of two bucket mechanisms each connected to a
tilting head on which a mercury switch is mounted. The upper
assembly , traps small gas bubbles generated by an incipient
fault and if sufficient gas has been collected, it closes a
contact and sounds a hooter in the control panel in the
SUBSTATION. The lower assembly which is directly in the path
of the connecting pipe operates when there is a serious
internal fault like a short circuit between phases , coils
or turns, earth fault, arcing or puncturing of bushing
insulator inside the tank. This liberates a considerable
amount of gas, and the displaced oil and gas surge through
the connecting pipe, and impinge upon a deflection plate
fixed on the lower assembly in line with pipe. This tilts
the Mercury switch which in line with the pipe. This tilts
the Mercury switch which in turn trips the circuit breakers.
The buchholz relay also detects accumulation of air on
account of low oil level, or faulty oil pumps. A per cock is
provided on the top of the housing to draw samples of
accumulated gas for analysis. An inspection window shows the
amount of gas which has accumulated. Provision is made for
manual operation on the alarm and tripping mechanisms to
facilities testing. A better method is to pump air through
the pet cock
Ref- Dr G.V Rao Phd
If any other result please send to my id -
mastalinprabu@gmail.com
With thanks
M.STALIN
| Is This Answer Correct ? | 2 Yes | 1 No |
description about dry type transformers
following are the questions asked in interviews: 1) Considering the short circuit fault, which switchgear is preferable, SFU OR MCCB? Which operates faster? whicg one is popular in Indian Market and why? 2)Define SCPD. What is type2 coodination? 3)Why the contactor rating is higher for the fuseless selection than for fuse selection? whether the ratinf of SFU or MCCB remains the same in both the cases? 4)If the HP rating is known then can you calculate the ratings of L.V Switchgear(SFU/MCCB, contactor, OLR) without using the selection chart?
in our 6.6kv motor feeder[it is having two sources from Bus A&B] earth fault relay is acting, we checked CBCT connection and cable meggerd values found very good still earth fault acting during first two are three start after that it will hold. please clarify what was the reason. if same motor is starting from other Bus-A it will start.
how much earthings are provided for 22KV HT Metering Kiosk
1 Answers GE, Gionee, Knight Frank, TATA, Vacmet,
HOW isolation transformer works.
selection of conductor in different voltage?
What are the weight of 800KV DA,DB and DC type tower ?
what is the Excaste meaning of CT Saturation?? 10 P 20, 15 VA, what is the meaning of 10, & 20. if the CT polarrity changed what will happened?? what is the differece between measuring CT & Protection CT?? what is the Saturation Point of measuring CT & Protection CT??
Neutral to earth and phase to earth voltage how much.
what is the use of vector group in transformer. means what r the application of various vector groups?
circuit breaker is ...............connected with circuit
Why the design of electromechanical energy conversion machines is based on the medium of conversion as megnetic field not as electric field?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)