How the oil level of the Buchholz Relay come down.

Answers were Sorted based on User's Feedback



How the oil level of the Buchholz Relay come down...

Answer / sajid hussain

When load increase on the secondary side of the
transformer,heat produced which decompose the oil i.e
hydrogen and carbon. This lightly Hydrogen gas entered in the
Relay Dom and produced pressure on oil at the upper side. The
oil level of relay housing decrease.If the heat produced is
too higher due to current flow or arc the decomposition of
oil is also high which cause the more oil level down in the
relay housing.
Note Any correction please send email
msajid1980yahoo.com

Is This Answer Correct ?    4 Yes 0 No

How the oil level of the Buchholz Relay come down...

Answer / guest

The Buchholz relay functions by making use of the liberated
gas inside the transformer due to an internal fault, to
actuate an alarm or trip the circuit breaker depending on
the seriousness of the fault. The virtue of buchholz relay
is that it detects an incipient fault i.e in the very early
stage itself before serious damage is done, whereas others
relays operate after the fault has occurred. Therefore
repair measures are simpler. Example of incipient faults are
short circuited core laminations, broken down core bolt
insulation, failure of inter turn insulation and consequent
local over heating , bad switch contacts and faulty joints etc..
The relay comprises a cast iron housing inserted in the pipe
connecting the transformer tank with the conservator tank.
It consists of two bucket mechanisms each connected to a
tilting head on which a mercury switch is mounted. The upper
assembly , traps small gas bubbles generated by an incipient
fault and if sufficient gas has been collected, it closes a
contact and sounds a hooter in the control panel in the
SUBSTATION. The lower assembly which is directly in the path
of the connecting pipe operates when there is a serious
internal fault like a short circuit between phases , coils
or turns, earth fault, arcing or puncturing of bushing
insulator inside the tank. This liberates a considerable
amount of gas, and the displaced oil and gas surge through
the connecting pipe, and impinge upon a deflection plate
fixed on the lower assembly in line with pipe. This tilts
the Mercury switch which in line with the pipe. This tilts
the Mercury switch which in turn trips the circuit breakers.
The buchholz relay also detects accumulation of air on
account of low oil level, or faulty oil pumps. A per cock is
provided on the top of the housing to draw samples of
accumulated gas for analysis. An inspection window shows the
amount of gas which has accumulated. Provision is made for
manual operation on the alarm and tripping mechanisms to
facilities testing. A better method is to pump air through
the pet cock
Ref- Dr G.V Rao Phd
If any other result please send to my id -
mastalinprabu@gmail.com
With thanks
M.STALIN

Is This Answer Correct ?    2 Yes 1 No

How the oil level of the Buchholz Relay come down...

Answer / m.stalin

dear mr Sajid Hussain your id wrong

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

to vary valtage from 0 - max a variac is necessary . so how to design for high power applications nearly about 200KW power

0 Answers  


Can we use Ccapacitive voltage transformer directly for metering purpose?

0 Answers  


What technology is used in latest generators?

0 Answers   IBC,


How does "OUT OF STEP" relay ,for Synchronous motor protection, work?

0 Answers  


if the number of poles generated in stator and rotor side of an induction motor are different then what will happen and why?

0 Answers  






How do we calculate conductor size?

1 Answers   Hero Honda,


in the directional overcurrent and earthfault protection,normally we are setting the angle 45 deg lead for phase fault overcurrent and -45 deg lead for earthfault fro forward direction.but both the fault are operating on the same angle region only.why?how the relay will response?

0 Answers  


What are the factor to be consider for CT selection in 132kV substation?

0 Answers   ABB,


what is the rating of Insulation tester for measure 15 KW, 3 phase 415V 50 HZ induction motor?

2 Answers   ABB,


On Which Pressure PRV is operated.

0 Answers   AEPL,


How LT megger works ?

0 Answers  


what is the use of power factor ? where its applicable ?

4 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)