the input mechanical power of a single alternator is
increased,its RPM increased but in case of an alternator
synchronised with grid its RPM does not increased with
increase of input mechanical power. why?
Answers were Sorted based on User's Feedback
Answer / ck misra
when the mechanical input to an alternator connected to
grid is changed it temporarily does increase the speed(RPM).
But an increase in speed means consequent increase in
frequency(as N=120f/P and P being the no. of poles is
constant)of the alternator.Now we know that the voltage and
frequency of grid busbar(what we call infinite busbar)are
constant(off course within some tolerance limit)and the
whole system has large electrical inertia which tends to
oppose any change in voltage level or frequency. So the
alternator is pulled back to synchronism by the grid.
BUT in case of stand alone alternator there is nothing to
pull the alternator back to synchronism and we can increase
the speed with a consequent rise in frequency....
Is This Answer Correct ? | 22 Yes | 1 No |
Answer / madhu balaji
whenever there is change in mechanical input to the
alternator, there will be change in rpm. but when it is
synchronised with busbar, there will be change in real
power shared by that alternator(i.e. when there is increase
in input, then real power shared by that alternator also
increases and vice-versa)
[similarly when excitation level of particular alternator
(synchronous generator)is changed, then reactive power
shared by that machine will be changed.]
Is This Answer Correct ? | 5 Yes | 1 No |
Please send specifications for 1000KVA dry type transformer or where I can get the specifications?
what happens if DC earthing and AC earthings are shorted?
what is the pressure of vacuum circuit breaker
we all know that both the generator and motor are electromechanical conversion devices.....then why we rate motor in kw and generator in kva????
Why Ac Systems Are Preferred Over Dc Systems?
how to calculate cable size, olr rating, contactor rating and mccb rating,to below given details three phase motor 75 kw,415 v,.85 pf,50 hz?
Where the Dry type tranformers are used.
Why field resistance is greater than the armature resistance in dc mechine
1 Answers Cape Peninsula University of Technology,
Can you explain about Restricited earth fault protection scheme
Explain the function and difference of Restricted earth fault, simple earth fault and sensitive earth fault with connection diagram.
What are the advantages of speed control using thyristor?
how much air gap in induction motor as per the Indian standards?