Answer / ck misra
when the mechanical input to an alternator connected to
grid is changed it temporarily does increase the speed(RPM).
But an increase in speed means consequent increase in
frequency(as N=120f/P and P being the no. of poles is
constant)of the alternator.Now we know that the voltage and
frequency of grid busbar(what we call infinite busbar)are
constant(off course within some tolerance limit)and the
whole system has large electrical inertia which tends to
oppose any change in voltage level or frequency. So the
alternator is pulled back to synchronism by the grid.
BUT in case of stand alone alternator there is nothing to
pull the alternator back to synchronism and we can increase
the speed with a consequent rise in frequency....
| Is This Answer Correct ? | 22 Yes | 1 No |
Answer / madhu balaji
whenever there is change in mechanical input to the
alternator, there will be change in rpm. but when it is
synchronised with busbar, there will be change in real
power shared by that alternator(i.e. when there is increase
in input, then real power shared by that alternator also
increases and vice-versa)
[similarly when excitation level of particular alternator
(synchronous generator)is changed, then reactive power
shared by that machine will be changed.]
| Is This Answer Correct ? | 5 Yes | 1 No |
How does the phase sequence controller works, how it identifies the phases? confirm working principle
What is the difference between Split ring and slip ring?
What happens with squirrel induction machines if the ends of rotor conductors are kept open? Explain
how to calculate size of cable from motor current given and how to calculate full load current of a induction motor.
What is the difference between MCB and Earth MCB? What is the working principal of MCB?
Is there any scope for an electrical engineer in MRF company......
i have a motor 55kw how u will calculate cable specification for this motor
pleasee tell me the risks and hazards of a Cable Jointer job? Thank you.
why CFL lamp requires less electricity than a normal lamp?/
What is the disadvantage in proportional controller?
I have a question, I visit 01 site and face a problem, there is 2.5 ton Air Con working, when air con compressor is running at that time rectifier voltages are increasing upto 290-295 v and rectifier is giving main high alarm (rectifier is APC single phase), before starting compressor rectifier voltages was 230v. when air con is going off rectifier voltages are decreasing smoothly at its actual voltages 230v. Load on Genset phases is this: Red-13.5 amp AC (Air Con load), Yellow-1.7 amp AC (BTS lights etc.) and Blew-4 amp AC (telecom system load), Genset phase to phase and neutral to phase voltages are also ok. These are 10 sites having same system and same rectifier APC brand at every site 02 genset are working but the problem is same at all these 10 sites. What will be the reason behind???
What will happen if i connect two 3-phase tranformers secondary supply on one bus bar that is R-Y-B-N?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)